Short circuit current on the load side of buck-boot transformer (autot

Short circuit current on the load side of buck-boot transformer (autot

Short circuit current on the load side of buck-boot transformer (autot

(OP)
I need to calculate the SSC on the Load of an autotransformer.
Any help would be appreciated
 

Ohm's it not just a good idea, Its the law.

RE: Short circuit current on the load side of buck-boot transformer (autot

Hello,

You need to have the following data:

Rated power of the transformer
Rated voltage of the windings
Impedance (Short circuit voltage)

With these values you may get a shortcircuit current value that will give you a "good reference" (infinite bus).

You typically determine the nominal current and divide it by the impedance (in per unit), this will be the shortcircuit current magnitude for a three phase fault.

Regards,

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources