I am mulling over the situation where an FPE designs a project that is bid out and built without the same FPE involved in construction support. The dilemna is the designer of record is no longer involved, it is in the contractors hands. However, a FPE is needed to sign off on the prelim and final acceptance tests.
Q1: What approaches have you seen for this situation?
Q2: Would you as an FPE be comfortable simply signing your signature (but not placing PE seal) to the final acceptance test report, and providing written certification that the sprinkler system is installed in accordance with the contract requirements?
Q3: Would you be comfortable placing a submittal review stamp on the shop drawings if the sprinkler sub were to sub the engineering to you?
Thanks!





RE: question for the FPEs
Q1: The FPE, who witnessed the testing should review and accept or reject the test results. It does not have to be the same FPE, who designed the system. Some local authorities may have a say in this. Also what is a sign off? Review and comment is one thing. I would not stamp and seal any test results unless they were performed by me (or I am the testing company).
Q2: NO.
Q3: Yes, if I was contracted to review the shop drawings and I agree with it. Only thing to watch out for is the conflict of interest. Let everyone involved know what is going on.
Rafiq Bulsara
http://www.srengineersct.com
RE: question for the FPEs
"Also what is a sign off?". The FPE would be required to simply put his/her signature on the test reports, to show that he/she has reviewed and accepted the reports.
RE: question for the FPEs
Rafiq Bulsara
http://www.srengineersct.com
RE: question for the FPEs