Metering CT
(OP)
Hi, I am looking for help locating an "off the shelf" outdoor rated CT. I am fairly flexible on the output and ratings. I would like to find "anything" low cost (<$150/unit) that could monitor load current 0-2000A @ 38kV with better than 5% accuracy.






RE: Metering CT
RE: Metering CT
Most donut style CT's are rated for 600V and can only be applied at higher voltges if the high voltage wire is insulated or the CT is on an equipment bushing, like a transformer terminal.
RE: Metering CT
You might be able to get a sensor for less, but you won't be able to monitor "0-2000A".
RE: Metering CT
RE: Metering CT
RE: Metering CT
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Metering CT
How accurate does the metering need to be to achieve your goal? Is it revenue metering with money changing hands, check metering to see if the revenue metering is accurate or just an indication of the approximate loading on a circuit?
For example, if the goal is to mesure transformer losses by comparing the high voltage power to the low votlage readings, you need very high accuracy equipment and even then may not get good results. If the goal is only to see the load on a feeder within +/-10%, a different type of CT or clamp-on meter may be possible.
To help answer your question, a little more informaiton is needed.