Hi Guys have a wired question to ask.

need to know what the flow rate would be for the following:
Main Line 10"
Service line first 10 feet to curb valve is 3/4"
rest of service to house is 1-1/4" for 55 feet.

what is my actual flow rate at the end of the 1-1/4" line b/c of the first 10 feet being 3/4"
everything is k copper and static pressure is 85 psi at the end of the line.

totally stumped on this one
 
Replies continue below

Recommended for you

forgot to add that i need to have a minimum operating psi of about 55 psi
and this is a water service line from the town supply

thanks for your help in advance
 
use Hazen Williams equation to calculate the headloss. Add in a minor loss for the meter and any other fittings.
 
i don't know if i have all the information to complete that, any help would be appreciated.

thank you in advance
 
you may be able to get a maximum of 9 - 10 fps through the copper line which would give you maybe 13 gpm
 
i thought it would be much more, given its only traveling through 10 feet of pipe it would have very little friction loss.
 
You would probably be able to get 35 gpm through the pipes with a headloss of approximately 62 psi. If you started with 85 psi, that would leave you with around 23 psi residual pressure. The velocity in the 3/4-inch line would be 25 ft/sec.


Not sure what is the practicality of this theoretical calculation.

If you exceed the recommended velocity of 8 ft/sec in the copper tubing, then the copper tubing will corrode away in a short time.
 
bimr,

thank you for your real work answer, i noticed on the sheets you provided that it has an actual 50 gpm rating but that's with an open flow and no resistance. i think i will design the system around 20 gpm and be on the safe side.

thanks for all the input guys.
 
Not really sure what application that you have, but it must be noted that you will be operating well outside of the normal water velocity range of 3-8 ft/sec.
 