400V Supply on 380V motor

400V Supply on 380V motor

400V Supply on 380V motor

(OP)
will there be any long time effect if we connect 380V 60Hz motor to 400V 60Hz supply?

Thank you.

RE: 400V Supply on 380V motor

Lower pf, higher no-load current, higher iron losses, higher temps and hence lower life.

Where do you have 400 V, 60 Hz by the way ?

Muthu
www.edison.co.in

RE: 400V Supply on 380V motor

(OP)
400V 60Hz was the clients requirement and yes it is not a common voltage here in the Philippines. The motor was designed with triple voltage 220/380/440V 60Hz.

Are those effects will still happen even if the motor has 5% voltage tolerance?

RE: 400V Supply on 380V motor

My guess is that you are actually in luck.  Probably actually about a 205/410V motor with that name plant.  380V is less than 8% down at 380 and less than 8% up at 440V.  Those three voltage probably only involve two different connections.  

RE: 400V Supply on 380V motor

(OP)
the motor connection are delta-delta/wye-wye/delta 220/380/440V respectively.

 

RE: 400V Supply on 380V motor

Quote:

the motor connection are delta-delta/wye-wye/delta 220/380/440V respectively.
Then you don't have a problem at all! Connect the motor for 400V operation. Since you have a double-delta connection for 220V - change the connection to double-wye (1.732X220 = 380V), about 5% over(400/380).
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources