Precast Mix Design Help.
I just start working for concrete company and i need a little help. i got a request for a tunnel mix design and i made one according to the specs. i received. but i would like to know what you guys think about my mix design.
1 YARD FT3
Cement 450 ASTM C-150 TYPE I / II 2.29
SLAG 450 ASTM C-989 FDOT APPROVED 2.47
57 ROCK 1500 ASTM C-33 9.48
PEAROCK 0 ASTM C-33 0.00
SILICA 1250 ASTM C-94 FDOT APPROVED 7.58
WATER LB. 265 ASTM C-260 4.25
ENTRAPED AIR 1.00% 0.27
Admix 1 49.00 OZ. WRDA 64 WATER REDUCER
Admix 2 0.00 OZ. DAREX AEA
Admix 3 24.00 OZ. ADVA 120 HRWR
Admix 4 5.00 GAL. DCI-S 0.67
Unit wt 145.0 YEILD 27.00
Water Cement 0.34
SLUMP 4 INCHES MAX
HERE'S THE SPEC.
Service life: 150 years
Environment class: External surfaces against ground: Extremely aggressive / Tidal zone no barrier
Internal surfaces: Slightly to moderately aggressive / not in contact with water/ Condition within 800 m from Ocean.
Nominal Cover: External surfaces: 2 inches
Internal surfaces: 1.6 inches
The covers must be assessed among calculation using life 365 model.
An over design might be applied, as set tolerances, for construction.
Density: ≥ 144 lb/ft3 [2300 kg/m3]
Class: V (Special) ≥ 6000 psi
apply an over design requirement of plus 1400 psi
Early strength (12 hours) shall be assessed on the base of compressive test results for the proposed concrete mixes.
Chloride content: ≤ 0.34 lb/yd3 [0.2 kg/m3]
Cementitious: ≥ 752 lb/yd3 [445 kg/m3]
Cement: OPC Type I/II – AASHTO M-85
Addition (Pozzolans and Slag-Std Specs - 346-2.3):
Cementitious replacement shall be assessed among calculation using life 365 model and mix trials adjustments to verify the properties of the fresh concrete.
o 20% Fly ash (FA- Std Specs -929-2) – 7 to 9% Silica fume (SF - Std Specs -929-3)
Or
o 60% GGBSlag (S - Std Specs -929-5)
Or
o 50% GGBSlag (S - Std Specs -929-5)- 10% Fly ash (FA - Std Specs -929-2)
W/C: ≤ 0.35
the ratios may be optimized among mix trials adjustments and calculation using life 365 model.
Corr. Inhibitor: ≤5 gal/yd3 [25 l/m3] (Std Specs -924-2.7)
the quantities may vary among calculation using life 365 model
Superplasticizer: HRWR (Std Specs -924-2.6)- to be defined kg/m3
Slump of maximum 4 inches [100] mm. Tixotropic properties are required to achieved good mould filling under external vibration
Retarder: WRR (Std Specs -924-2.4) - to be defined kg/ m3
Slump retention ½ hour
Placement: N.A.
Laboratory trial mixes must be conducted on the basis of measurement of properties of the fresh concrete. This shall permit to optimize the use of superplasticizer and retarder.
Aggregates: Fine aggregate (Std Specs -902): DOT Natural silica sand
Max size coarse aggregates (Std Specs -901): 3/4" - Limestone size No. 67 or eventually 57
1 YARD FT3
Water Cement 0.34
SLUMP 4 INCHES MAX
HERE'S THE SPEC.
Or
Or
W/C: ≤ 0.35
Placement: N.A.
RE: Precast Mix Design Help.
Your percentage of slag will cause a slow strength gain, so be prepared for low 7-day and possibly lower than anticipated 28 day strengths.
The specified cover is not consistent with their description of an aggressive environment...it should be more.
How will the concrete be placed? A 4-inch slump can be difficult to place.
If you do not have a record of service for this mix design, then you will have to go through a trial batch procedure and apply an overdesign factor (which is specified at 1400 psi, but you don't know if that's enough)
this is for a pre-cast structure, so optimum curing conditions might speed up the strength gain. It might be good to ask your client how fast they want to strip the forms and how they plan to cure. that may affect your mix design.
as for cvg's comments about fly ash, it is optional as far as i can tell.
Density of the concrete can help the low cover issue, but not in a very aggressive environment.