Disconnecting Multiple Motors with One Switch?
Disconnecting Multiple Motors with One Switch?
(OP)
I have an application where I need to disconnect and lock out four VFD motors (all are 3 HP) with one switch. But I have been unable to find a suitable switch. Does anyone know of a switch that might work?
This switch is to allow the operator to lock out four sections of belt drivs so that he/she can step out onto the belts to adjust or repair sheets of wood veneer. The operator's switch is only for "minor servicing activities, performed during normal production operations, and are routine, repetitive, and integral to the use of equipment for production."
All motors are independently controlled by their drives. We thought about disconnecting a common power feeder to the drives but the VFDs (A-B 700) would then require too much time to restart. We will have 30A NEMA-style disconnect switches for each motor for servicing the belts or motors.
This switch is to allow the operator to lock out four sections of belt drivs so that he/she can step out onto the belts to adjust or repair sheets of wood veneer. The operator's switch is only for "minor servicing activities, performed during normal production operations, and are routine, repetitive, and integral to the use of equipment for production."
All motors are independently controlled by their drives. We thought about disconnecting a common power feeder to the drives but the VFDs (A-B 700) would then require too much time to restart. We will have 30A NEMA-style disconnect switches for each motor for servicing the belts or motors.





RE: Disconnecting Multiple Motors with One Switch?
Perhaps four contactors with a single switch. Use a switch with early contacts to disable all the drives before the contactors dropout. Otherwise, someone is sure to hit the switch with the drives running which invites a bunch of failed drives. This scheme also provides some redundancy in keeping the motors from running by disabling the drives AND disconnecting the power to the motors.
The conveyor doesn't need the drives to prevent roll back does it?
Keith Cress
kcress - http://www.flaminsystems.com
RE: Disconnecting Multiple Motors with One Switch?
Disconnecting power to a group of motor starters is common but the motor starters must be approved for group fusing.
The VFDs may be unhappy if a disconnect between the drive and the motor is opened at an inappropriate time.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Disconnecting Multiple Motors with One Switch?
We'd take two contacts from the keyed switch to a safety relay wired to the safe-off input of the four drives. With the relay de-energized, power would be removed the gate circut on the drives. We dread the thought of going to OSHA with this for their approval...
RE: Disconnecting Multiple Motors with One Switch?
PaulBr.
RE: Disconnecting Multiple Motors with One Switch?
Our standard is to incorporate an Aux switch on our disconnects so that the drive "knows" that we are disconnecting the motor. Saves us from a lot of drive faults.
Lots of switches could be used for this with the conductor size and load, but as you point out, I haven't found any that are approved motor disconecting means.
RE: Disconnecting Multiple Motors with One Switch?
To meet motor's local disconnect requirement of NEC and since OSHA is applicable, your options are limited to:
1. Disconnect the main common feeder to the VFDs. If it is not within sight, you need to lock it OFF.
2. Provide separate disconnects at each motor and if any one of them can start the belt, you need to lock OFF each one of them too if all are not within sight. (Hopefully VFDs are turned off before the maintenance need).
Contactor/relay rig would not meet the intent of the Code for having a local disconnect, imho. In fact it would be no different than a starter/controller.
Rafiq Bulsara
http://www.srengineersct.com
RE: Disconnecting Multiple Motors with One Switch?
That is too similar to the old stop/locks that were once used for safety lockoffs.
This was a cheap addition to a standard industrial class stop button. With the stop button depressed, the device could be flipped over to hold the stop button down. There was provision to then install a padlock to hold the button down and prevent unauthorized operation.
In Western Canada when I was just getting into industrial work, the legislation was changing and these devices were no longer being accapted as a safe lockoff device. Wye? Not safe, to many failure modes. to many people injured and killed.
Any OSHA officer who approves a lock-off device other than a complete disconnect of all energized conductors may not understand his job very well.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Disconnecting Multiple Motors with One Switch?
Semiconductors aren't normally accepted as isolation devices because they have off-state leakage and don't introduce a physical air gap. I'm amazed if OSHA would allow a semiconductor as a safety isolation, but I don't think they do. Maybe I'm wrong?
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Disconnecting Multiple Motors with One Switch?
"Drives or solid state output devices designed for safety related function shall be allowed to be final switching element, when designed according to relevant safety standard"
This was added in NFPA 79 of 2007. I was working for printing press manufacturer and this was relief for us. We have been using this function on Rockwell PowerFlex drives, Control Technicues drives, and Indramat servo drives without disconnecting power.
RE: Disconnecting Multiple Motors with One Switch?
Do let us know when you eventually have an incident due to a failure in a control circuit.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Disconnecting Multiple Motors with One Switch?
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Disconnecting Multiple Motors with One Switch?
Use 4 pole Isolator after the VFD output and take one phase from each motor and pass it through the Isolator.So by this way you disconnect one phase of each motor by one action as well as the motors will not getting start with two phase.
Best regards
RE: Disconnecting Multiple Motors with One Switch?
Use 4 pole Isolator after the VFD output and take one phase from each motor and pass it through the Isolator.So by this way you disconnect one phase of each motor by one action as well as the motors will not getting start with two phase.
Best regards
RE: Disconnecting Multiple Motors with One Switch?
Local motor "disconnect" is a requirement, just de-energizing is not sufficient.
HRSADI: That would be single phasing,a no-no.
Rafiq Bulsara
http://www.srengineersct.com
RE: Disconnecting Multiple Motors with One Switch?
RE: Disconnecting Multiple Motors with One Switch?
We are still going to have traditional 30A NEMA disconnects for each motor for servicing. We will be fully compliant with NEC requirements.
All our disconnects have an aux contact back to the drive or PLC to indicate to the control system that the motor switch is open.
Please read the quote again in my first post. That language is directly from OSHA that permits "minor servicing" without full lockout. IEC has similar language in their standards.
If the gate circuit is disabled, the motor can't turn if the output transistors short. Induction motor can't turn with DC.
Because our state has it's own OSHA, we have to request a variance to use a safety relay system with the A-B drive safe off feature. While this type of system is widely used in Europe, it is rare in the US. "Selling" it to OSHA will be time consuming and difficult.
Those of you who haven't heard of safety relays or safety PLCs, should take some time to do some internet research. Just Google "safety relays" and you'll find lots of links that describe how these very clever systems work. I wish our OSHA people would do some research, too...
To avoid having to go to OSHA, I was hoping someone could direct me to a motor switch with four sets of three phase contacts (or some way to stack them) that could be opened with one motion. However, I am prepared to make our case to OSHA that a safety relay and the safe off feature meets the "minor servicing" requirements.
Again, I'm very pleased at the responses in this thread and I am very grateful for all your ideas.
Thanks!
RE: Disconnecting Multiple Motors with One Switch?
Companies like this will build you whatever you want. I would get a base mounted switch and a padlocakable operator, I would also get another contact that operates prior to any of the others opening that I would wire to the Safe Off circuits of the VFDs. That will also ensure that nobody opens that switch under load.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: Disconnecting Multiple Motors with One Switch?
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Disconnecting Multiple Motors with One Switch?
Thanks!
RE: Disconnecting Multiple Motors with One Switch?
Another manufacturer of very good switches is Craig & Derricott - similar to the K&N range but in my opinion of a slightly better build quality. They also make some pretty big multipole switches - 6 poles at over 100A for sure, perhaps bigger than that. I've nothing against K&N, I've used plenty of their stuff too and it is very good.
Jim,
Totally agree about safety relays. They're a great product when applied correctly. My previous comments re. disconnectors / isolators was with respect to making safe for direct contact with conductors, not rendering the machine unable to run which is a very different requirement. Apologies if I misunderstood your aims.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Disconnecting Multiple Motors with One Switch?
C&D looks like a nice line, but not available in the US. They probably don't have UL and don't want to go to the expense.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: Disconnecting Multiple Motors with One Switch?
My state has had a NRTL excemption for "Industrial Electrical Equipment" in state law for many years. Should I find that the C&D switches will work and they'll ship to us directly, the lack of a NRTL label will not preclude their use in our plants.
RE: Disconnecting Multiple Motors with One Switch?
Also check with your insurance company first. Some underwriters put in a clause that has weasel words to the effect of "damage from a fire determined to be caused by a non-evaluated piece of equipment will not be covered."