Basler DECS-200N to ControlLogix Prosoft - Modbus

Basler DECS-200N to ControlLogix Prosoft - Modbus

Basler DECS-200N to ControlLogix Prosoft - Modbus

(OP)
I'm having trouble writing a setpoint to the DECS-200N via a Prosoft MVI94-MCM module.  I am able to read values over the Modbus link (RS-485) but I am having trouble writing a setpoint to it.  I continue to get an error code of 3.  I'm curious if anyone has had success using a Prosoft Modbus card in a ControlLogix system to write setpoints?  Any and all helpful would be greatly appreciated!!

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

Haven't done your specific application before but I've used a prosoft modbus scanner on a compact logix to a number of VSD's with out any issues.  But modbus error code 03 is as follows:

03 ILLEGAL DATA VALUE A value contained in the query data field is not an allowable value, because it is one of the following:
• Outside min. or max. limits.
• Parameter is read-only.
• Message is too long.

Are you trying to write the voltage setpoint or a power factor setpoint?, What mode of operation is the DECS in?

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

(OP)
Right now I'm trying to write the FCR setpoint.  Once I prove I can get that working, I'll then move on to Voltage, PF and VAR setpoints.  The DECS is currently in FCR mode.

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

So your trying to write to address 47621 and 47622, is your address offset correct?, some modbus implementations add 1 to the address.  Also this is a floating point value, and the DECS is expecting to see valid data in both registers.

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

(OP)
This is correct, I'm attempting to write to address 47621 and 47622.  My command list is:

[Commands]
#         Internal      Poll    Reg  Swap     Node  Modbus  MB Address
# Enable   Address  Interval  Count  Code  Address    Func   in Device
START
       1         0       1     57     0        247       3        7250
       1         1000    1     5      0        247       16       7561
       1         1020    1     4      0        247       16       7620
END

The 1st 2 commands work fine, the 3rd one is the problem.  As you can see, I only have a reg count of 4 as I'm only trying to do the FCR setpoint right now.  My line of code in the ControlLogix is:

COP(TEST_REAL_2, MCM.Data.WriteData[20],2);
TEST_REAL_2 is a "REAL" value

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

What is the actual value of TEST_REAL_2 that you are trying to send?

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

(OP)
First - sorry for posting multiple threads.  I thought I'd try the the other forum for further expertise - I just signed up for this yesterday so I'm learning.

Anyhow - I have varied the value of "TEST_REAL_2" from 0 to 5000 with no luck in the DECS.  I continue to get an error code of "3" - Illegal Data Value.

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

I'm guessing the real format in ControlLogix is not the same as the floating point format used in the Basler, so you get error code 03. A little internet research should help you figure this out.

http://www.digi.com/wiki/developer/index.php/Modbus_Floating_Points

The link under "See Also" at the bottom of the page may be helpful.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

(OP)
xnuke - thanks a ton!!  This website helped.  However, I'm still having trouble.  I swapped the words (low word first) and I'm able to write the FCR setpoint.  Since that worked, I increased my "REG COUNT" in the Prosoft module to 4, so that it would cover the AVR setpoint as well.  As soon as I increase the REG COUNT to 4, I get an error code of 3.  I then tried to set up a separate command just for the AVR setpoint, but had the same outcome.  Any ideas?

[Commands]
#         Internal      Poll    Reg  Swap     Node  Modbus  MB Address
# Enable   Address  Interval  Count  Code  Address    Func   in Device
START
       1         0       1     57     0        247       3        7250
       1         1000    1     5      0        247       16       7561
       1         1020    1     2      0        247       16       7620
END

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

lobear71..

Did you get this resolved?

CH

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

(OP)
y2khines - yes, I did.

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

How did you resolve it?
Thanks

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

(OP)
The first step was to break the "REAL" values into 2 "INT" values - this was done using the COP instruction.  Next, the 2nd INT was moved into the first register, and the 1st INT moved into the 2nd register:

Step 1:
COP(SETPT, SETPT_INT[0],2); /Example Setpoint

Step 2:
MCM.Data.WriteData[xx] := SETPT_INT[1]; // Low Word
MCM.Data.WriteData[yy] := SETPT_INT[0]; // High Word

RE: Basler DECS-200N to ControlLogix Prosoft - Modbus

Thanks for the feedback. Sorry I didn't reply after my last message. I've been on vacation and away from a computer.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources