Masonry Wall Design
Masonry Wall Design
(OP)
Looking at designing a load bearing, masonry wall in a high wind area. Wind Load is 37psf, wall is 17' tall. For the sake of simplicity for my question, I'm treating the roof load as negligible and only using wind loads.
Going through the TEK manual, I get a #5 @ 24" o.c. from the allowable stress design tables.
**16,039lb-in/ft required, 16,420lb-in/ft provided
When I do strength design per ACI530...I get (without any reductions, yet)...33,374lb-in/ft provided. The formula I used is Mn=(Asfy)(d-(a/2))
I thought maybe instead of fy=60,000psi, I should've used Fs=24,000psi but that yields 14,118lb-in/ft. Do the 2 methods yield these drastically different results or have I made a mistake? I also cannot seem to "back calculate" the allowable stress tables.
Thanks for the attention. JEW
Going through the TEK manual, I get a #5 @ 24" o.c. from the allowable stress design tables.
**16,039lb-in/ft required, 16,420lb-in/ft provided
When I do strength design per ACI530...I get (without any reductions, yet)...33,374lb-in/ft provided. The formula I used is Mn=(Asfy)(d-(a/2))
I thought maybe instead of fy=60,000psi, I should've used Fs=24,000psi but that yields 14,118lb-in/ft. Do the 2 methods yield these drastically different results or have I made a mistake? I also cannot seem to "back calculate" the allowable stress tables.
Thanks for the attention. JEW






RE: Masonry Wall Design
Are you sure you are using the proper equation from ACI-530?
I think you should be using EQN 2-17 or 2-18.
RE: Masonry Wall Design
RE: Masonry Wall Design
RE: Masonry Wall Design
I, too, thought I should use Fs, not fy, however eq 3-27 & 3-28 both use fy. **3-27 and 3-28 are the equations I used to get the numbers above. 33,000 lb-in/ft is using fy and 14,000lb-in/ft is using Fs. Makes a big difference!!
RE: Masonry Wall Design
RE: Masonry Wall Design
RE: Masonry Wall Design
RE: Masonry Wall Design
Ref. section 3.3.4.1.1
RE: Masonry Wall Design
I too see why the strength design is "stronger" than asd. I realize it's not when you add in the factors. Thanks for everyone's help.
RE: Masonry Wall Design
RE: Masonry Wall Design
http://www
http://www
Never did get a good answer.
RE: Masonry Wall Design
RE: Masonry Wall Design
I only use the strength design allowables when I'm in pretty desperate straits.
RE: Masonry Wall Design
-More "accurate"
-Much harder to do a quick calc by hand
ASD
-Proven to work for a long long time
-Easy to do a quick calc
They're not really related to each other at all. It's an analog to concrete design (or steel design for that matter). They're just two different methods of doing the same thing.
With a taller, more slender wall (h/t>30), the strength method may be the only option as the ASD method starts to get pretty conservative for slender walls.
Yes, the do yield different results. As slickdeals said though, for strength design you have to multiply your wind by 1.6. 25,000 lb*in/ft demand versus 33,374 lb*in/ft capacity. For ASD it was 16,039 vs 16,420. Not as drastic a difference as you had in your OP.
RE: Masonry Wall Design
LRFD is based on the ultimate strength methodology similar to concrete where Whitney's stress block is assumed and both the steel and masonry are brought to ultimate capacities to determine the nominal strength. ASD is based on a simple elastic stress distribution using conservative allowable stress values.
I recently compared design results and there is a surprisingly large disparity between the two methods. Apparently, you can get by with a lot less if you use LRFD to design masonry. It prompted me to started a thread about the noted difference as well.
http://www
I still like to use ASD because the quality of masonry construction is so poor. We have been making a significant efforts in recent months to crack down on special inspection requirements and idiot-proof some of our typical details to circumvent some problems. However, there is only so much you can do when the masonry sub barely looks at your drawings. You can't be out there every day.