osha regs and cable clamps for suspension cables for a suspended scaff
i am designing a scaffold that is suspended by cables.  we are planning on using specific lgt cable chokers with thimbles as required per osha but i am wondering  if the "fist grip" clamps can be used instead, to make enable the height adjustment to be easier.  at first i was thinking they were not allowed, but after further reading in the regs, it appears that they are.  if we use them they would have to be torqued after loaded then before every shift.  Crosby recommends 3 clamps for a 5/8" cable but i am wondering if more clamps are required since it will be supporting people
what are your thoughts?
thanks
RE: osha regs and cable clamps for suspension cables for a suspended scaff
1926.451(d)(12)
When wire rope clips are used on suspension scaffolds:
(i) There shall be a minimum of 3 wire rope clips installed, with the clips a minimum of 6 rope diameters apart;
(ii) Clips shall be installed according to the manufacturer's recommendations;
(iii) Clips shall be retightened to the manufacturer's recommendations after the initial loading;
(iv) Clips shall be inspected and retightened to the manufacturer's recommendations at the start of each workshift thereafter;
(v) U-bolt clips shall not be used at the point of suspension for any scaffold hoist;
(vi) When U-bolt clips are used, the U-bolt shall be placed over the dead end of the rope, and the saddle shall be placed over the live end of the rope.
1910.28(p)(5)
    When a hanging scaffold is supported by means of wire rope, such wire rope shall be wrapped at least twice around the supporting members and twice around the bearers of the scaffold, with each end of the wire rope secured by at least three standard wire-rope clips.
29 CFR 1910 is general industry, and 29 CFR 1926 is construction industry.
TX pretty much hit it on the head.
I noticed you said something about chockers - just make sure they can't "bite" into the material they are choking.