CT secondary winding 5A. vs 1A.
Hi guys,
our power transformers, 6.6kV/433V needs to be protected against restricted earth fault (87N) and standby earth fault (51G) and is connected in a 6.6kV HV switchgear.
at the onset of the project all the secondary winding of the protection ct is 5A. There was a change in the design of the HV switchgear and all the secondary winding of the protection CT's are now 1A (except for the 87N & 51G). The transfo manufacturer have already purchase the 5A CTs. My question is, can we still use the 5A CT's? the protection relay in the HV switchgear is a SIPROTEC 7UT613.
thanks for any input.
RE: CT secondary winding 5A. vs 1A.
May be, but I would do the right thing and replace the CTs with 1A secondary.  (or replace the relays with 5A secondary)
Rafiq Bulsara
http://www.srengineersct.com
One other possible solution would be an interposing CT, but performance would need to be evaluated for effect on phase angle (affects differential), saturation, etc.  I suspect Rafiq's solutions are best though.
Yup, already talked to our system engineer and we do have to replace the 5A Cts.
Thanks for the input guys!!!