Fault Analysis Help
Fault Analysis Help
I am investigating a fault on a 4.16kV 2300hp motor and was looking to get opinions on the attached event report showing the fault.
The fault happened on the motor and blew all (3) power fuses on the motor contactor, tripped an upstream breaker protected by a Multilin 750 relay, and tripped the utility circuit switcher. There are obviously some coordination issues that need to be addressed, but I am also trying to make sense of the events as they occured.
In looking at the attached event report from the main breaker I have the following observations:
It appears that the system was operating with steady state current up until point (1) on the event waveform at which time there was a current transient with the current on all three phases increasing. I am assuming that this current transient is a result of the fault at the motor. This current transient only lasts for about 1/2 cycle before the current returns to steady state. I am trying to figure out why the current returns to steady state value so quickly, and the only thing I can think of is that after the 1/2 cycle falut transient the fuses at the motor blew returing the current seen at this breaker relay to steady state current at point (2).
At point (3) it appears that the current goes to zero and looks as if this is the point the breaker opened. The event report shows the relay tripping the breaker on an Neutral Time Overcurrent trip (51N). The part that is confusing is why there are about 3 cycles of steady state current after the current transient before the breaker appears to trip (between points (2) and (3)) The only thing I can come up with is that during the transient the relay pick's up and issues a command to the breaker to trip and these 3 cycles of steady state current is seen due to a 3 cycle delay for the breaker to clear. In other words although the downstream fuses at the motor cleared the fault and returned system current to steady state, the realy had already issued a breaker trip command and the breaker clearing time had about a 3 cycle delay before it actually opened. Does this make sense?
The breaker trip output is "Output 3" seen at the bottom point (4) and can be seen issuing the trip command and then dropping out after the breaker appears to open. This trip output appears to be on for about 3 cycles while the breaker clears. I believe 3 cycles may be a typical clearing time for a vaccum type breaker?
The voltage waveform at point (5) shows a small transient at the time of the current transient or fault. There does not appear to be much of a distortion or drop however and I wanted to see if this made sense? Could this be due to the fact that the fuses cleared the fault current so quickly?
The strange part is what happens to the voltage waveforms after the breaker appers to open. When the breaker opens at point (3)/(4) the current drops off however the voltage appears to taper off slowly. The voltage is coming from a set of PT's on the switchgear bus located on the secondary of the breaker that is opened. Why would the voltage appear to taper off slowly for several more cycles as opposed to going to zero right after breaker opening. The voltage tapers off to where at point (6) it is about 3kV and at the last cycle shown of the waveform the voltage is slightly under 1kV. What could cause the voltage to drop so slowly?
I appreciate any suggestions or corrections on this event as I am trying to make sense of what happened. Thanks for the help.
RE: Fault Analysis Help
After the breaker tripped, it's likely there were other motors on the system that continued spinning and producing voltage due to their residual flux.
Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.
Other stuff: the relay is tripping in about a cycle. I wonder why the 51N element has been set with no delay. It seems that the breaker is operated by the 51N starting signal. It could be the reason of the mis coordination.
Yes this breaker is serving other loads in the plant.
Excellent point about motors on the system generating voltage with their residual voltage after breaker tripped. There were several 500hp+ motors running on the system at time of fault.
My relay did not show me the value that the 51N element saw. The 51N pickup was set at 150A. The relay however does give me the individual phase currents and angles at the time of the 51N pickup. Can I add these phase current vectorally to arrive at the value of ground current that the 51N element saw in its residual calculation?
Something else that has me curious is the fact that the main relay picked up on a 51N element (ground fault) although looking at the current waveform it shows that the fault at some point turned into a three phase fault. The relay did not pick up at all on a overcurrent condition for this 3 phase fault. Is it possible that the relay picked up on the 51N element first an iniated the trip to the breaker before it regognized a phase fault condition? In other words if the relay has already picked up and issued a trip command from one of the elements will it ignore the pickup from any other elements that may occur after?
As AMBMI suggested, it seems like 51N is much too fast.
Alan
I am still waiting on utility relay event report but from what they have told me they picked up on a ground current as well. I'll let you know what I find.
Am I right as far as adding the phase currents and angles vectorally to see what magnitude the relay picked up on?
I dont know if I totally understand a 3 wire 51N residual calculation. I always thought this would only show current if there was current flowing outside of the three phase conductors ie a neutral or ground current. Are you saying that this can pickup current unbalanced phase current in the three phases only? Can you briefly explain how this calculation works?
Does the fact that a 51N element can pickup on steady state unbalanced conditions factor into the pickup. I imagine it must to avoid nusience tripping. 5% minimum pikup seems like a number that comes to mind.
That makes sense about the fuses blowing. I guess with the fuses blowing at different times this caused the current magnitudes on each of the three phases to be different and thus trigger the 51N element.
Can you please elaborate more on this CBCT. Are they similar to GFCT? Actually we had some trips on a Main breaker at a sub which feeds a few pumps and a feeder.
Trips actually started recently when more 1 phase transformers were added to the feeder.
The main breaker for the sub has a 351S which has inputs from both a GFCT(50:5) and 3 phase CT's (1200/5). The settings of 50N1 was 20A and 40cycles time delay. It tripped on IG being 24A.
I am reluctant to increase the setting to more than 50 as the system ground fault is already limited to 100A. If more resistance is added to the ground fault return path through arc resistance then there is a chance that ground faults are not sensed...
I want to learn more abt the GFCT's. Does it have the capability to measure phases?? How is it adding the 3 phases vectorily??
I am not trying to deviate from the original thread... but sense that the issue i brought was related to GFCT too. If you guys need i can start a new thread...
gokul
The CBCT that David was talking about is a toroidal CT that encloses all three phases (and neutral if necessary). It sees the flux summation of the three phases. If current are equal, there is no net flux and the CT has zero current. If there is current imbalance, whether due to a fault, or unbalanced loading, it will see the resulting net flux and the secondary current will be proportional to the imbalance.
David Castor
www.cvoes.com
Much better the response of the core CT. So less problems and a smaller threshold but an additional stuff (the core CT) is needed.
Regarding the Gokulkrish2 trip I would say that 24 A of ground current with 100A as max grnd short circuit current are a lot. The element has also a great 40 cycles delay so any transitory should be gone. I would expect that the system experienced a real fault. Critical point: the 50/5 core CT is quite small, here we are more used to see 100/1 core CTs, more iron better performances..
For a measured ground fault current using a separate residual CT in the neutral bonding jumper, there is a separate input connection and is designated as 51G in SR 750.
All mfrs are not the same. See thread238-238200: Earth fault protection.
Rafiq Bulsara
http://www.srengineersct.com
Plus I was particularly responding to:
and in reference to SR 750.
Without a neutral connection to loads (3-wire circuit), the sum of three phase currents will always be zero in normal conditions.
Rafiq Bulsara
For a residual CT configuration used for this 51N function the three phase CT's sum the current in the three phases. Since these three CT's are connected in a wye configuraton then for any unbalance there would be current flowing in the neutral of the CT connection. This current flowing in the neutral of the CT connection is where the relay element would pickup this unbalanced current. This would be similar to adding a neutral to a 3 phase wye connected load, where any unbalanced current on the phases would flow in the neutral. This neutral current would flow for unbalanced conditions aside from fault conditions? Is this not correct?
If a newer solid state relay (such as 750) does not have an element in the neutral CT connection but rather uses a vectoral summation of the 3 phase currents wouldn't you expect the same results? Esentailly the vectoral sum of phase currents indicates the current flowing in the neutral. This would hold true if there is indeed a neutral present in the priamry circuit but what about this case where there is no neutral present on this 3 wire circuit? Shouldn't this vectoral sum still provide a neutral current value even for unbalanced conditions that are not a ground fault?
Now with a zero sequence CT (core CT) I always thought that this was strictly only picking up on ground currents. That even under unbalanced conditions the net flux in the core was zero due to the fact that the unbalanced current was still being balanced on the return legs and therefore the net flow through the core is zero. I am starting to wonder now if this is true? Is this not true and the zero sequence CT will sum the flux of the current and output a neutral current value if there is any unbalance.
I am still anxiously awaiting utility relay report.
Rafiq Bulsara
I can understand what you are saying in concept but cant seem to visualize it.
Let me present an example:
We have a 3 wire 3 phase load with unbalanced currents. We have 3 CTs (one on each phase) connected in a wye configuration measuring current. As you said because there is no neutral in the primary circuit then there will be no neutral current flowing in the CT secondaries and therefore not neutral current flowing in the CT connection neutral.
Now lets say we go ahead and connect a neutral to the primary load so that the unbalanced phase current flows in this neutral. Now since there is neutral current flowing in the primary circuit we will see neutral flowing in the secondary CT circuit from what you are saying. However the phase angles of the current through the CT did not change and therfore the phase angles of the current in the CT secondaries did not change. So then how by having neutral current in the primary does this effect the netural in the CT secondaries?
The realy gave the pickup currents of:
Ia = 5973A @38deg
Ib = 6798A @169deg
Ic = 6000A @ 270deg
The relay did not give a 51N current value but adding these vectorally I come up with 2,244A as the pickup value. Clearly these currents here are shown to be unbalanced however we cannot tell if there was actually a ground fault presnet from these phasors.
Rafiq Bulsara
Thank you very much for your help I appreciate your input you have offered thus far. Of course I do not expect you to solve this mystery over the internet however I do appreciate your thoughts thus far on a general idea of what might have been going on. I am bringing a knowlegable consultant on-site to review this event and others with me however I wanted to hear others thought on this site to get additional input/ideas.
I finally got the relay event files from the utility relays and have posted these files. The 501-2 relay is looking at the utility transformer high side, low side, and tank ground CT's. The 387E relay is looking at the utility transformer high side, low side, and line side of the NRG CT between the NGR and the neutral bushing.
It appears that the utility circuit switcher opened when the 501-2 relay picked up on ground current. This relay input is looking at a CT which is around a 4/0 bare length of copper connected to the substation ground grid and bonded to the transformer tank. As you can see from the attached plot this CT saw about 250A of current through this CT. I am trying to think why this CT would see this current and the only thing I can come up with is the possibility that the path through the ground grid, through the transformer tank and back to the ground grid to the NGR presents a low impedance path that allows this ground current to flow through this path. I am not really familiar with the function of a tank ground CT. What typically is the purpose of a tank ground CT? Should it see current for a fault downstream on the system?
This tank ground CT has a very low pickup value (20A) and thus falls below the pickup value of my main breaker and downstream feeder breakers. I'm thinking the reason this tank ground CT has such a low pickup is due to the fact that it is not supposed to see much fault current during the fault? If this tank ground will see substantial fualt current during a fault then this pickup probably needs to be coordinated with the downstream ground pickups. I am going to discuss with utility but wanted to hear others thoughts.
It appears that the CT on the NGR saw about 50A in the neutral during this event. The other thing that strikes me as strange is the fact that the NGR saw 50A while the tank ground saw 250A. Assuming that all the ground current must return to neutral bushing through the NGR I do not see how the additional 200A going through the tank ground is getting back to the neutral. In this case I am thinking there is a shunt path around the NGR that is allowing current to flow back to the neutral.
The 387 relay is also looking at the load side of the NGR between the NGR and the ground grid. While the CT on the line side of the NGR saw 50A this CT on the load side of the NGR only appears to see about 0.5A. These currents on the line and load side of the NGR should match and I find it strange that they dont. Another question for the utility.
I'd appreciate greatly any additional input based off this new information and thank you greatly for your help.
Alan
I am confused as well about the tank ground. I am going to question the Utility about its purpose.
Thanks for your input.
In my experience in switchyards, older transformers were mounted on railroad wheels and tracks for easy removal for repair and maintenance. The wheel bearings were insulated so the ground CT was the only connection to ground for the tank. The winding neutral and arrestors were grounded separately. Any current flowing in the ground CT had to be from an internal transformer winding failure. The relay pickup could be set quite low, because there should never be any current except for internal faults.
(A ground fault in a 208V radiator cooling fan will also trip off the transformer. We discovered this on a retrofit.)
If an arrestor or neutral got bonded to the tank, or a conduit support or other ground path connected the tank to ground, a circulating current might flow. Maybe someone didn't like seeing only one ground on a transformer and added another, creating a ground loop that carries current during an external fault.
The 64 protection is also used on rectifier units, high voltage boilers, and some utility's live tank circuit breakers.
Thank you for your insight.
Upon inspection of the substation I found that there were two tank sides of the transformer that had a bonding connection to the ground grid which is right in line with what you mentioned about a ground loop carrying current during an external fault. I guess its possible that the path from the ground grid to one side of the tank transformer case around the transformer case and back to the ground grid through the connection on the other side may have a low enough impedance that is a lower impedance path than other paths between the ground grid and NGR that current flow through this path during an external fault. Even if this did occur however I would expect to see all of this current travel through the NGR to the neutral of the transformer. Even if we removed one of the (2) tank ground connections I still suspect that there could be circulating currents through the remaining tank ground connection and through the transformer concrete foundation which I'm sure presnets a pretty low impedance path to ground as well.
I agree with your comment on being able to set this relay pickup very low if the tank was isolated from ground (insulated from foundation) and only had one connection due to the fact as you mentioned the only current that would be flowing through this CT would be from an internal winding fault. Because of the fact that this existing connection seems to create a low impedance path for current to flow during an external fault the pickup will need to be coordinated with the downstream pickup if this relay does indeed see this circulating current.
One other thing that I noticed during inspection was the fact that there was a single phase single bushing station service transformer that was connected to the neutral on the line side of the NGR and on the transformer the primary and secondary neutral was bonded together. The secondary of the transformer then went on to feed a station 120/240V feeder panel which appeard to have this secondary neutral bonded to ground inside the panel with the ground of the panel then tied into the substation ground grid. Seeing this I guess it is possible that current flowing on the ground grid from an external fault can travel up the ground connection to the feeder panel through the bonded neutral in the panel back to the severice transformer secondary, through the bonded primary/secondary neutral connection on the service transformer back to the neutral of the utility transformer completely bypassing the NGR. The neutral wire on the secondary of the 120/240 transformer is only #10 or so for large fault current we would expect to see some damage if current was indeed taking this path. But if were only talking about 200A or so as shown in the event report then I guess its possible. Something to investigate further with the Utility.