How do you determine control cable length and size for a cable that runs from a DC source (125V) to some relay inputs like SEL or GE Multilin?
 

RE: Control Cable Size and Length

Length? Long enough to reach from the 125VDC battery distribution panel to the relay.  You will have to look at your project's physical layout drawing and estimate the wire length.

Size? - If it is a power wire to deliver power to the relay, a #12 or #14 AWG size wire is probably more than large enough to carry the load without appreciable voltage drop.  If it is just an input signal, like breaker position indication, the current draw is so small that a #18 awg is large enough but it might not have the physical strength to withstand the wire pulling stresses during installation.

Your question leaves a lot of assumptions to be made or questions unanswered.  What are you worried about? Voltage drop to the relay input? Voltage drop during tripping? How much wire or cable to order for the new substation?  

RE: Control Cable Size and Length

(OP)
rcwilson,
First of all thanks for your response. What I am worried about is the distances wires have to cover in high voltage yards to reach from control center to equipment in the yard. Sometimes these distances can be in upwards of 1000ft and my question is at what point do you go with a size higher than let's say #14 or #12. For example if you run a #12 wire from the breaker to the control center for tripping, closing and auxiliary contacts then at what distance would it become unreliable, where something like a #10 would be required. I am not running a single conductor from the yard to the control house to be worried about pulling strength, it would be more like an 8 to 12 conductor cable.
 
 

RE: Control Cable Size and Length

For circuits delivering significant current such as trip/close circuits, you'll need to do voltage drop calculations. Select the wire based on the minimum design control power voltage and required operating voltage + a safety factor. I don't think there's a rule-of-thumb.

For signal circuits where operating time is critical, you should evaluate the affect of capacitance of the wiring.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources