Eccentric Weld Shearing
I'm trying to find the resistance of the welds on a shear tab. Table 3-34 of the CISC Handbook seemingly gives me exactly what I am looking for, but I have also seen the resistance calculated by using table 3-27 and setting k=0. This is what is done in the AISC Manual. Unfortunately, I do not acheive the same result. For example. For a length of weld l=152mm, size D=6mm, and a 12mm thick plate, eccentricity to bolt lines e/l=a=0.4, table 3-34 gives C'=0.935, which gives a resistance of P=0.925x152mm= 142kN. Table 3-27 gives C=0.222 which gives a resistance of P=0.222*6mm*152mm= 202kN.
Which is actually giving me the resistance of the welds?
-K
-K
RE: Eccentric Weld Shearing
Table 3-27 is for a different situation where the eccentricity of load is measured normal to the plates.
BA