Drain Seal Pot Design

Drain Seal Pot Design

Drain Seal Pot Design

(OP)
Hi,

I am wondering how to design a open drain seal/fire pot (installed for hazardous drain system)and what is the criteria that determines the water seal level? Is there any standard that is applicable to such?

Regards,
UKD

RE: Drain Seal Pot Design

A parallel situation is the water seal in a flare drum to prevent flash back.
Looking in my notes, reference "A" calls for 6-inch min submergence.
Reference "B" calls for 3-4 inch submergence.
If your concern is flashback prevention, 3-6 inches of water seal should be a good design.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources