Interaction of Duct Fittings

Interaction of Duct Fittings

Interaction of Duct Fittings

(OP)
Hi! Could somebody help me regarding this?

All of the data on loss coefficients are based on fully developed flow of air into the fittings ( free stream loss coefficient ). Air leaving fan, elbow, tee or any duct fittings is always turbulent and distorted. You actually need a certain length ( 5 to 10 dia in duct lenght ) for the flow to fully develop. If the air flow does not become fully developed the pressure drop of the downstream fittings will generally increased including noise.

I am actually looking for methodology / reference or books that tells you how to calculate or compensate for fittings installed very close to each other. Using the loss coefficent for fully develop flow is inaccurate.

I have tried ASHRAE and It does not tell you about this problem.

Thank you

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources