(OP)
Probably an over simple question for the plumbers in here but I need some clarification on any rule of thumb or thoughts on what is a reasonable length of straight run of 4" dia. PVC at 2% slope from a toilet pan to a septic tank, that is assuming there is a maximum length.
Thanks

RE: gravity sewage line

There really isn't a rule of thumb for maximum length - it all depends on the particulars of the installation.

You will have two issues;

1.  Final invert at the septic tank.
2.  Solids settling out in the pipe.

With a long run, you will have a deeper pipe connection on the septic tank the farther you run the pipe.  Septic tanks have to be pumped - and sometimes maintained - so the deeper it is - the harder it will be to maintain.

The longer your run - the more likely solids will settle out before they reach the septic tank.  Having a lot of fixtures that flow water without appreciable solids (showers, mop basins, etc.) help push the solids down the line.  Extra water closets discharging to the line also help.

A 2% slope will cause the solids to travel farther on less water - but will also cause the final pipe invert to be twice as deep as the standard 1% slope allowed for 4" pipe.

Code (at least the IPC) require cleanouts every 100 feet to help push the solids along if they start clogging the pipe.

I have seen runs as long as 1000 feet - but there were other fixtures discharging water into it, the final invert allowed for it, and there were a good quantity of cleanouts.

RE: gravity sewage line

(OP)
Thanks for the precise and useful information - a * for you.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources