Hi,

can any body explain the application of under current protection in capacitor bank feeder?

RE: Under Current Protection Application

Overcurrent maybe?

RE: Under Current Protection Application

Possibly to detect open capacitors.?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Under Current Protection Application

Hi.
Yep, Bill you are right!!!

RE: Under Current Protection Application

(OP)
thanx all,

Bill & Slavag
unbalance protection will detect open capacitor.

is it the same application?

 

RE: Under Current Protection Application

Hi SMB1.
Is not same application.
Undrcurrent protection is detected disconnection of capacitor bank and prevent a reconnection with some timer.
Is operated only if ALL 3-ph currents are below some set point ( of course not before connection of CapBanks).

Unbalce protection base on the meas in the CT installed betwen two starpoints of banks.

Best Regards.
Slava
 

RE: Under Current Protection Application

I'm afraid I've never heard of anyone applying undercurrent protection to a capacitor bank.

I would expect that the capacitor can would fail shorted and an overcurrent condition would be detected.

Can you explain where this is used and how the undercurrent condition ignores normal load current?

RE: Under Current Protection Application

The undercurrent would be looking for something sufficiently less than normal load current.  Fused cans will fail to an open condition and current will go down.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources