Attaching the shear wall etension to an existing roof diagram
2

Attaching the shear wall etension to an existing roof diagram

Attaching the shear wall etension to an existing roof diagram

(OP)
I designed this detail to provide shear wall extends to the existing roof diaphragm. (see attached). Is there a "liquid nail" or similar glue with approved shear values to be used as a replacement to the fastening from above the roof sheathing to prevent from disturbing existing roof cover? Is there a better way of continuous connection between the shear wall and the roof diaphragm?
Thanks!

If pdf attachment is not accessible, here is additional information:

framing:
Roof rafters 2x6@16"o.c. 16GA metal channels
wall studs 2x6@16"o.c. 18GA metal channels
#7 SD screw for roof diaphragm to blocking fastening
 

RE: Attaching the shear wall etension to an existing roof diagram

I prefer mechanical connections for this application even if a glue could be shown to do the job.

An expert is a man who has made all the mistakes which can be made in a very narrow field

RE: Attaching the shear wall etension to an existing roof diagram

I assume reasonable thickness sub-flooring or roof diaphragm with rigid insul. above; screw up into diaphragm through new cold formed stl. blocking members with short screws.  Use a 6" Zee, and offset top flange wrt wall below, so screwing up through top flg. is easier to get at.  Otherwise, end detailing of blocking Zee's is a you show for your 6" C blocking.

RE: Attaching the shear wall etension to an existing roof diagram

Unless it is a tested and approved connection, I do not believe that glue can be considered in the shearwall shear values.  Mechanical only.

Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask

RE: Attaching the shear wall etension to an existing roof diagram

(OP)
Using Zee for blocking is a great tip. Thank you for that. I have also thought about using short screws from the attic side but it would be almost same as using glue, since screw heads are on the wrong side.
I am going to try that hoping the inspector will take it easy.
Thank you again!   

RE: Attaching the shear wall etension to an existing roof diagram

I think screws as suggested by dhengr are your only option if connecting from the bottom.  But I this only works if there is insulation above the diaphragm so you can penetrate the plywood.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources