Thief Hatch &Vent
Thief Hatch &Vent
(OP)
Can anybody tell me how to check if a vent and thief hatch combined on a 400 bbl atmospheric storage tank will be sufficient to relieve any sudden pressure surges/vapor breakthrough?
Thank you,
Thank you,





RE: Thief Hatch &Vent
The hinge offers additional resistance to opening.
The hinge force is hard to predict due to friction & rust.
There are also possible spring forces depending on the model.
Any resulting flow through the device must be reduced by 50% (per OSHA) because it has no vendor calibration.
Using a thief hatch to "officially" protect a tank from overpresssure is highly questionable.
As an engineering professional my recommendation is to put aside this activity.
RE: Thief Hatch &Vent