 What is the maximum diameter of a main sewer pipe that a lateral sewer pipe (house connection pipe) can be connected? For example, is it possible a DN 200mm pipe, connect to DN 1600mm main sewer pipe?

Are there any standards for the max. pipe dia.?

thanks for the replies...

RE: Max. dia. for the main sewer line + house connection

200mm is quite large for a lateral to a house, I would recommend 100mm. Yes, a 200 could connect to a 1600, but you need to get a permit first to do this as this is a very large sewer. A 1600 sewer sounds like a regional interceptor and I would be surprised if they want individual laterals connected to it.  

RE: Max. dia. for the main sewer line + house connection

A residence is typically on a DN 100-150mm service.

The problem that you run into is that standard fittings are not readily availabe for the larger pipe diameters. A service connection would have to be installed using a chimney tap or some other connection. The chimney tap arrangement is expensive. The interceptors are usually much deeper as well. Again, it will be expensive.

Below is a link to common pipe fitting dimensions:

http://www.hobas.com/index.php?eID=tx_nawsecuredl&u=0&file=fileadmin/user_upload/hobas%20digital/HOBAS%20GRP%20Tees.pdf&t=1275691384&hash=3a7e264cda636f897bf5b312b6ade2f0

Typically, the local sewer collection authority will not want service connections on the large diameter interceptors. Interceptors usually have the manholes farther apart and are installed with less slope than laterals

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources