Framing Angle - 1 bolt each leg

Framing Angle - 1 bolt each leg

Framing Angle - 1 bolt each leg

(OP)
Can experienced wood designers please comment on the acceptability of this connection.

Basically I have a preexisting suspended ceiling which has worked for the last ten years. Myself and a builder where walking on this ceiling and it was certainly strong.

Being asked to certify the existing structure, I have investigated the structure and found the existing connection to consist of 2-skewed nails. Doing the calculations, I did not feel this connection had the required capacity so have specified framing anchors with 2-bolts each leg. I only received one bolt each leg.

I can justify to myself that this connection can work transferring shear with bearing on the wood.

Would this connection detail be acceptable to most?

All comments are appreciated.

Regards

RE: Framing Angle - 1 bolt each leg

Can you add lag screws to the missing holes?

RE: Framing Angle - 1 bolt each leg

What did you ask for and what did you pay for - 2 bolts or 4 bolts installed??

RE: Framing Angle - 1 bolt each leg

Asixth:
A lag screw might work in the ledger beam, but it would split the end of the joist member.  I would drill and use a bolt there.  Bolts generally have a little more cap'y. than lag screws.  Is this the same ceiling as had the bent .25" hanging rods from a purlin web?

RE: Framing Angle - 1 bolt each leg

asixth...the plate is too small to be very effective for anything but marginal shear loads. It's better than toenailing.  Why the bracket instead of a joist bucket?

Also, don't get lulled into thinking that something is "design" strong just because it didn't move under your weight.  You're thinking like a contractor...think like an engineer....it hasn't yet seen its design loads.

RE: Framing Angle - 1 bolt each leg

(OP)
dhengr

Good pick up. It is the same ceiling.

RE: Framing Angle - 1 bolt each leg

I agree here with Ron.  A top hung joist hanger with the flanges turned in would have been a much better connection.

If I understand the relationship of the two members, I would not be concerned with the edge distances as it appears to me that it could be adequate for the bolt size seen.  However, the built-in entricity of the connection concerns me.  It will induce horizontal splitting with time.

Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources