comparison between motors

comparison between motors

comparison between motors

(OP)
I have two motors Existing & New motor

New Motor
460 V Delta,60 HZ,cos Phi=0.89, Current : 18A 11 KW
IP 55 81 KG  S1  1M B3 60 HZ rpm : 3515
160M-PB01Z-V
DE 6309 ZZ C3 DIN 625
NE 6308 ZZ C3 DIN 625
Make : SCHORCH


Existing Motor
460 V Star, Current : 16.8A   11KW
IP W55  SI UT Grade deg centigrade
S1 21362 4  Ins class F/B  rpm: 3526
DE: 6309 Z/C3
NDE : 6309 Z/C3
Wt : 105 KG
Make : ABB

Are these motors one to one replacement. The new motor is Delta connected.Above which rating you need Star/delta starter.How to know the frame size is same , both are 160M

Thanks
 

RE: comparison between motors

If frame size is not given measure the shaft height.
Below 37.5 kW you seldom have to worry about reduced current starting. At 37.5 and above look for a different method of reducing the starting current. Star delta is falling out of favor because of the current spike at the transition and the availability of soft starters.
Comparing the rated currents and rated speeds, it appears that the proposed replacement is a higher slip motor and it may be a 1.1 service factor motor.
IT DEPENDS
In some applications this may be a drop-in replacement.
In some applications the overload device may have to be adjusted for the higher current although this is a good idea in any case.
The conductors should be reviewed to verify that they have adequate ampacity for the higher current motor. This is more of an issue in Canada than the US. Check your local code.
Speed and slip. In many applications close enough is close enough, but for speed critical applications the slightly lower speed and higher slip may cause issues.
 

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: comparison between motors

The Scorch motor is a European 160M frame. The ABB motor should have a type number somewhere - post a photo of the nameplate if you have one.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: comparison between motors

Also, I suspect that 11kw motor is NOT 105kg!  Otherwise, looks like pretty much the same motor for any ordinary application.

The ABB motor is Class F insulation with Class B rise so it is pretty conservatively rated thermally.  I don't see any Insulation Class or thermal data on the Schorch motor.

RE: comparison between motors

Quote:

Also, I suspect that 11kw motor is NOT 105kg!
Here is a 15hp 3600 rpm that weighs 237 pounds = 107.5kg
http://www.baldor.com/products/detail.asp?1=1&page=1&;catalogonly=1&catalog=M2394T&product=AC+Motors&family=General+Purpose|vw_ACMotors_GeneralPurpose&hp=15&rpm=2800-3600&winding=07WGW677&rating=40CMB-CONT

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: comparison between motors

Hmmm! Pete.  Seemed a bit heavy but maybe not.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources