Hello
I am interested in learning how industrial motors (1000HP to 50,000 HP MV to HV)and their supplies are connected. More specifically I would like to know if the neutral of the motors and the newtral of the supply side are grounded. Also how does the neutral connection/grounding approaches differ from Asia to Europe and North/South America ? Your help and opinion is much appreciated
Best regards
Karim

RE: Floating or grounded neutrals on motors and supplies

Grounding of motor neutrals is a bad idea unless you want to sacrifice motor thermal capacity in an attempt to balance unbalanced supply voltages.
Supply grounding  and grounding methods depend both on protection philosophy and the type of supply.
Wye or delta/ primary or secondary/ solid ground, impedance ground, corner ground, no ground, zig-zag grounding or wye:delta grounding.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Floating or grounded neutrals on motors and supplies

I agree with Bill.  Within our plant auxiliary power distribution system our plant (US) we have a variety of supply systems: solidly grounded supply systems (480vac), ungrounded supply systems (480vac), high resistance grounded systems (4kv) and low-resistance grounded systems (13kv).  In all cases, the neutral point of a motor wye connection is left floating.   Bill points out one good reason, system unbalances would result in much higher motor current unbalance since the motor attempts to generate a balanced three phase voltage.  

An interesting thing about motor dynamic analysis (such as Krause), it seems to assume the motor neutral is connected back to the supply system.  This seems a very wide assumption for motor simulation but I haven't ever heard of matching practice.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Floating or grounded neutrals on motors and supplies

(OP)

Many thanks to Bill and Pete. Your answers are most helpful. If one could develop a 1000 times more sensitive ground fault or stator insulation leakage current differential CT, on what motors could one use it ? I was askd this question at a recent IEEE on Motors and Gens Conf.
Thanks
Karim

RE: Floating or grounded neutrals on motors and supplies

I think it would be very useful as an alarm feature for critical motors (or better yet if continuous leakage value is available, use it as a trendable parameter).   That would be a useful warning that some investigation is required.  

On the other hand, using a more sensitive trip function wouldn't benefit most applications - certainly where loss of motor impacts the process severely.  Also with existing ground fault trip the damage is limited to the winding, not the core.  The improvement I guess would be to be able to save the winding...I'm not sure if this benefit would offset the disadvantage of more trips.

Going back to the benefit of early warning, we had two instances of intermittent ground fault trips, after which motor tested fine and ran fine.  These were warnings that something was going on.

One turned out to be a quarter inch hole in the groundwall insulation at the very bottom of the knuckle on bottom end of vertical motor.  It never went hard ground and didn't show up on insulation tests, but when we opened it up we saw it. There had been water in the motor at some time and apparently dripping from knuckle to ground plane below created a fault that blew open that portion.

Another turned out to be a cable splice fault on 15kv cable for 13.8kv system.  Actually the EPR cable tested 30 megaohms at 10kv, which we have come to accept as normal for these runs of cable 2000', sometimes wet.  But between 10kv and 15kv it broke over to zero ohms.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Floating or grounded neutrals on motors and supplies

Waross

Very intersting response, I was not aware of the two points you mentioned.

Can you quickly explain how grounding neutral point of motor helps balance unbalanced line voltages and how doing this incerases thermal heat in the motor?

RE: Floating or grounded neutrals on motors and supplies

The back EMF of the motor is balanced both in voltage and phase angles.
If the line voltage is unbalanced the mismatch will cause excess current. This crrent will be limited by the system impedance and the motor impedance. This is why a small voltage unbalance causes a large current unbalance.
The unbalanced current is in a direction to correct the voltage unbalance however the system impedance is often so low in relation to the motor impedance that there is little actual correction of the applied voltages.
In an instance where a large motor is supplied by a transformer with not much more capacity than the motor requires and with a relatively high impedance the correction of a voltage unbalance may be noticeable.
My comment concerning an "attempt" to correct unbalanced voltages was somewhat tongue in cheek. The attempt will usually yield so little effect as to be futile. The extra current will result in more motor heating and rotor heating may be be an issue also.
I have seen a "soft" distribution line with a unequal currents, voltages and the resulting displaced neutral corrected to a large degree by the action of a wye:delta transformer bank with the primary neutral connected. The KVA size of the transformer bank was significant compared to the KVA of downstream unbalance. The action has some similarities to the action of a motor fed by unequal voltages. The relative sizes of motors compared to transformer banks results in the corrective action of motors to usually be much less than the possible corrective action of a large transformer bank.
Again, yes there is some correction, but no, don't plan on it, it is usually not enough to be useful.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Floating or grounded neutrals on motors and supplies

(OP)
I understand then that we have a whole range of scenarios as far as neutral grounding on the supply side. With a floating one the differential current sensor shoudl not work as there is no return path of the leakage current to the supply.
Thanks for the info
Regards
Karim

RE: Floating or grounded neutrals on motors and supplies

I'm sure you know, a standard motor differential can work with floating neutral - it just compares current flowing into line terminal of A phase with current flowing out of neutral of A phase (into the other two phases).   If there is a ground fault within the motor or phase-to-phase fault within the motor, a difference is seen.

Also I am pretty sure the grounded motor neutral is very rare if it exists at all.  I wonder what NEC would say about it? (I don't know).

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Floating or grounded neutrals on motors and supplies

Clarification in bold:
"Also I am pretty sure the grounded motor neutral is very rare if it exists at all. "
should read
"Also I am pretty sure the externally-connected motor neutral is very rare if it exists at all. "

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Floating or grounded neutrals on motors and supplies

I guess delta-wye starter with external running leads contradicts that.  Really what I meant to say is I haven't ever heard of connecting motor wye point to either ground or to any system neutral.   

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Floating or grounded neutrals on motors and supplies

I would let both statements stand, Pete, even with a star delta starter.
If a motor is large enough that differential protection is desired, it will be ordered with all winding ends accessible and suitable for installation of CTs.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Floating or grounded neutrals on motors and supplies

I voted for you in the IEEE DEIS election Karim. Maybe you can bring some more focus to rotating electrical machines (seems like most of the interest is in transformers and smartgrid).    

Anyone else in IEEE DEIS... you've got until 9/29 to vote.

=====================================
(2B)+(2B)'  ?

RE: Floating or grounded neutrals on motors and supplies

Once the differential CTs are sensitive enough to pick up the capacitive leakage current, there may be no point in further improvement in sensitivity.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Floating or grounded neutrals on motors and supplies

I thought the basis for the minimum differential setting is CT accuracy, rather than capacitive leakage current.

=====================================
(2B)+(2B)'  ?

RE: Floating or grounded neutrals on motors and supplies

Accuracy is good but when your setting must be above the level of the capacitive current, how many orders of magnitude more of resolution is really useful, or am I missing something?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Floating or grounded neutrals on motors and supplies

All I was saying was I was under the impression errors you have to assume for the CT's (including steady state and transient) are typically much higher than the cap current.   Maybe if you have very very long power cables inside the zone that might not be true(?).... but for our differential-protected motors the CT's are in the motor term box.  

=====================================
(2B)+(2B)'  ?

RE: Floating or grounded neutrals on motors and supplies

Correction:
"cap current"
should have been
"capacitive current"
(I am assuming no capacitors connected to ground of course)

=====================================
(2B)+(2B)'  ?

RE: Floating or grounded neutrals on motors and supplies

Hi Pete;
I was responding to this particular post:

Quote:

Many thanks to Bill and Pete. Your answers are most helpful. If one could develop a 1000 times more sensitive ground fault or stator insulation leakage current differential CT, on what motors could one use it ?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Floating or grounded neutrals on motors and supplies

Aha.  Sorry I had no idea of the context of your comments. Now it makes perfect sense.  My apologies.

=====================================
(2B)+(2B)'  ?

RE: Floating or grounded neutrals on motors and supplies

To summarize: If we wanted to improve sensitivity of differential protection there should be some gains possible if we had more accurate CTs. But not unlimited as you mention, since there are other errors (like capacitive current) to consider.

=====================================
(2B)+(2B)'  ?

RE: Floating or grounded neutrals on motors and supplies

(OP)
Dear Bill and Pete,
Many thanks for coming back to this topic and thread again and take time to help. I did obtain a lot of information from our field, service, installation and marketing guys on this. There is no standard way of connecting these motors even though this may sound very risky in some situations. Grounding of MV to HV neutral supplies is not always there (suprising). The more we learn about this the more surprized we are at how diverse approaches and practices are.
Thanks Pete for voting for me on the IEEE DEIS run. I am a rotating machine guy and I agree, focus is on other topics even if WE produce the MVAs ! All assests are important though of course.
The discussion on the differential CT sensitivity, capacitive and resitive insulation current values is the heart of the thread. I would just say that if we have a diff CT precise enough to give C and DF online then we would have IEEE286 ONLINE possible. A big deal I think.
Cheers
Karim   

RE: Floating or grounded neutrals on motors and supplies

Interesting. So the small primarily capacitive leakage current that Bill mentioned is what you would intend to measure accurately and compare its angle to the voltage to ground.  Sounds challenging to achieve that level of magnitude and phase accuracy, but I agree it would be a big reward.

=====================================
(2B)+(2B)'  ?

RE: Floating or grounded neutrals on motors and supplies

The capacitive currents in measuring C & DF are extremely small, typically in milliamps range. That's the reason expensive test kits like as ac schedring bridges are used. I don't see how CT's can come anywhere close to those measurement levels.

Muthu
www.edison.co.in

RE: Floating or grounded neutrals on motors and supplies

It may be worth looking into Ground Fault Interruption  devices.
A typical GFI receptacle in North America will be rated at 15 or 20 Amps but will trip at 15 milli-amps. There is your 1000:1 ratio.
I don't suggest using a GFI but the measuring methods may be scalable.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Floating or grounded neutrals on motors and supplies

There is also the matter of discriminating the phase of the ground current (differential current). 1 degree error would be a huge error in a power factor measurement.

=====================================
(2B)+(2B)'  ?

RE: Floating or grounded neutrals on motors and supplies

Just thinking out loud, I'm guessing gfci probably sends the main current directly through an operating and restraint coil (without any transformation).  Would be a challenge with higher voltages and currents since the amount of copper and insulation in that coil would be large. But you never know.

=====================================
(2B)+(2B)'  ?

RE: Floating or grounded neutrals on motors and supplies

Actually I have no idea how a gfci works but I doubt it has 2 coils as I suggested, so I withdraw my comment about gfci. Sorry.

=====================================
(2B)+(2B)'  ?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources