how to design SPUs for an Elevator room?

how to design SPUs for an Elevator room?

how to design SPUs for an Elevator room?

(OP)
does anybody know the rule of thumb for elevators rooms in designing its SPU. what is its TR/sq.ft

thanks guys

RE: how to design SPUs for an Elevator room?

I might, if I knew what a SPU was. A new acronym everyday, I love this industry.

RE: how to design SPUs for an Elevator room?

Yes, please tell us what SPU means, and you might also want to spell out TR.

Good on ya,

Goober Dave

RE: how to design SPUs for an Elevator room?

(OP)
SPU = split packaged unit

TR= TONs of refrigeration

please advice on the tr/sq.ft

RE: how to design SPUs for an Elevator room?

you should get data on the heat dissipation of the equipment, how often it runs, and do a normal load calculation.

There may or may not be a rule of thumb on ton/ft.. but that really can be wrong. I could imagine a high elevation elevator in high use buildings needs more cooling than a 2 story building elevator that has very efficient motors etc.  

RE: how to design SPUs for an Elevator room?

(OP)
i have 5-units of 35kw motor its high rise elevator. assume that its efficiency is 85% and its use factor is 95%. what formular for heat dissipation can i use?

RE: how to design SPUs for an Elevator room?

SPU only for elevator rooms ... means you dont have fresh air and only the evaporating unit is recirculating the air within the room

if thats the case and the elevator machine room is interior with only possible roof exposed...

these could be the good range.

0.49 - 0.53 TR/sq ft

RE: how to design SPUs for an Elevator room?

Rather than using a thumb rule, I guess it is quicker and safer to do a load calculation. All you need is to factor in the fabric load and the Motor Load. Fresh Air would be Zero. No Occupancy and minimal lighting.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources