Cable tension for railing guard
(OP)
Does anyone have a good way to calculate the tension required on a 3/16" cable that is acting as part of a guard at a stair opening? The cables are 3 1/2" apart and run vertically from the 1st floor to the 2nd floor ceiling, passing through sleeves in the end of each tread & the second floor. The maximum length of cable with no lateral support is about 7', & the spacing must be less than 4" to meet code requirements for a guard. This means they must be tight enough that they can't be pushed more than 1/4" sideways. The biggest problem is that all this tension is loading a new steel beam at the second floor ceiling level & I have to size that beam & carry that load down to the foundation. It is a renovation of an existing dwelling.






RE: Cable tension for railing guard
h
If I were to guess, it is going to be hard to meet the defelction requirements.
RE: Cable tension for railing guard
RE: Cable tension for railing guard
How is the cable anchored at the ends?
RE: Cable tension for railing guard
http://www.cablerail.com/standard/partslist.shtml
Consider a tensioning sequence, start at mid (center) of post work to top and bottom as shown in:
http://www
RE: Cable tension for railing guard
RE: Cable tension for railing guard
RE: Cable tension for railing guard
That is not a particularly good design solution, except to pull the 2nd fl. beam down, or the 1st fl. beam up. The forces don't have to go to found., they are all resolved internally in that frame, as long as the two beams and their columns or bearings can take the loads.
However cute or clever the Arch. thinks it looks, it just doesn't work well. You can't possibly tension the 3/16" cable enough to prevent the 1/4" lateral deflection. Do the statics: one leg of the right triangle is .25"; the other is (3.5' x 12 or 42"); that's 168 to 1, and the forces in the cable and laterally will be in these same proportions. A 2kip cable force will resist about 12 pounds lateral, and in the process the cable force will increase to (168.003/168)( 2k) or 2.04kips. You can't practically find a stiff enough beam and cable system to make this guard system work. Think about the cable for a minute, it just will not carry a lateral load until it is deflected a significant amount in proportion to its span length, and then it still takes a substantial force and reaction along its length.
That will make one hell of a harp though, if you tune it correctly.
RE: Cable tension for railing guard
If deflection is critical then cables are not the way to go.
A good Senior engineer would steer the architect away from this type of solution before it was fixed in their vision.
Propose a couple of solutions.
RE: Cable tension for railing guard
Most of highway stuff talks about energy absorption and a lot of cable stretch and deflection, and that's good for them because it does absorb energy, without a solid (brick wall) stop, and that's what they want to save people. That may teach you something about cable structures, but doesn't fit your needs very well. There is some literature out there on cable structures.
RE: Cable tension for railing guard
I told him he was going to have to tune it, since the first inclination of anyone using the stairs will be to strum it.
Thanks for the links boo, those fittings are much better than what the architect proposed, but it think nutte is right: a 4" sphere is going through regardless of the tension.
I guess I have to sell some aesthetic modifications to the architect.
RE: Cable tension for railing guard
If you go to a 2-1/2" spacing, you can then have an 11/16" deflection in the cable. At present, you can only have 3/16" deflection, so you can cut your pre-tension by a factor of more than 3 if you change the spacing.
RE: Cable tension for railing guard
The vertical spacing never exceeds 3" such that under reasonable conditions a 4" sphere will not pass through. We usually spec 300 to 400 lb cable tension each but I have no idea if anyone has ever read the note much less used it. End post moments from cable tension sometimes control. After pushing and climbing on them in the field I am much more comfortable with the concept. This is really an easy problem to over analyze (as I have in the past).
RE: Cable tension for railing guard
i'd set up a test for the arch to look at ... show him how easy it is to deflect a 7' span cable. let him wind up the tension, up a fish scale on it so he doesn't overload it.
would a clear plastic post be sufficiently invisible ??
RE: Cable tension for railing guard
This is open ended, what force must be resisted?
Think here about the practicality of tightening the cables; tighten one to a design tension, tighten a second one and deflects the members and reduces the tension in the first one, etc. etc.
Think of the stringer size, Using dhengr's 2k, even though it looks inadequate, you have almost 7k/ft upward preload on the stringer.
The good part about this preload is that a lateral force on a couple of wires would shorten them, increasing the uplift, causing a deflection which would ease the preload in the adjacent cables. That is, any cable that tried to shorten would tend to pick up increasing amounts of the total preload.
Michael.
Timing has a lot to do with the outcome of a rain dance.
RE: Cable tension for railing guard
Attached is cable deflection and loading info
RE: Cable tension for railing guard
RE: Cable tension for railing guard
RE: Cable tension for railing guard
The 2006 International Building Code (IBC) and 2007 California Building Code (CBC) require that guardrail intermediate railings be spaced so as to prevent a 4" diameter sphere from passing between the rails (IBC/CBC 1013.3). However, the code does not state what load is to be applied to the 4" diameter sphere. While such an oversight is not critical to solid railing members, it is of utmost importance in flexible railing systems such as wire-rope cables. In the absence of Code guidelines, a rational load must be developed.
They proceed to apply the 50 psf infill load to the area of a 4" circle, and double it for impact, resulting in 8.7 pounds force trying to push this 4" sphere between the cables. This is a rational approach, but the end result, 8.7 pounds, seems low to me.
RE: Cable tension for railing guard
RE: Cable tension for railing guard
RE: Cable tension for railing guard
I just talked to the architect again, he really doesn't want visible posts, so closer spacing seems to be our best option. The 4" spacing is to prevent children getting through it or stuck in it, the load that the guard has to carry is unrelated to the force required to push a 4" sphere between the cables. The cables will easily carry the required lateral load directly, although our code (Ontario) like IBC does not have any value for the force on the sphere.
For rb1957, the 1/4" deflection is the amount that adjacent cables have to deflect to pass the 4" sphere. Maybe your razor wire is best. I don't think I'd push on it with 8.7 lb force.
RE: Cable tension for railing guard
RE: Cable tension for railing guard
RE: Cable tension for railing guard
RE: Cable tension for railing guard
RE: Cable tension for railing guard