Hi guys!

Here is a question for short-circuit study experts.

A small plant is fed by a 750 kVA, Yg-Yg transformer. The utility wont give X/R ratios.

IEEE std C37-010 gives a typical ratio of around 7 for that transformer.

Given that X1/R1 ratio, is there a way to estimate the X0/R0 ratio?

RE: Question for short-circuit study experts

Figure that X0 is about 85% of X1 and R0=R1.

RE: Question for short-circuit study experts

(OP)
First, thank you for your quick reply.

Someone here told me the exact same thing but he wasnt able to tell me where it was from.

Is it form any standard?

Thanks again

RE: Question for short-circuit study experts

General empirical data.  Conrad St. Pierre's Short-Circuit book is a good source for such things.

RE: Question for short-circuit study experts

Check J & P Transformer Handbook and ABB Red Book.

RE: Question for short-circuit study experts

Hope you were referring to transformer X0/R0 ratio.For smaller 3 phase  units, 85 % of positive impedance is right as David pointed out. But if the unit is formed from single phase units or the transformer is a 5 limbed core unit( which will be the case with large 3 phase units say above 150 MVA)X0 will be same as X1.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources