Hi,
I have been hired by a contractor to explore options to widen and existing footing.
The contractor cast the the column eccentric to the footing. 12x12 r/c column on 5x5 footing but 1 foot from the edge. Bearing pressures now exceed allowable.
One option is obviously to demolish and another to underpin although I'm not to keen on this option.
I was considering another option of casting a jacket around the existing column (say 5" around) and attach the two with epoxy dowels. I would then consider pouring a new footing over the existing footing and with the the reinforcment in the "jacket" embedded in the footing. This new footing would now be centered on the column. I would also have to expoxy dowel the new footing reinforcing bars into the existing column.
Has anyone seen this type of detail before? Any other options?
Thanks
I have been hired by a contractor to explore options to widen and existing footing.
The contractor cast the the column eccentric to the footing. 12x12 r/c column on 5x5 footing but 1 foot from the edge. Bearing pressures now exceed allowable.
One option is obviously to demolish and another to underpin although I'm not to keen on this option.
I was considering another option of casting a jacket around the existing column (say 5" around) and attach the two with epoxy dowels. I would then consider pouring a new footing over the existing footing and with the the reinforcment in the "jacket" embedded in the footing. This new footing would now be centered on the column. I would also have to expoxy dowel the new footing reinforcing bars into the existing column.
Has anyone seen this type of detail before? Any other options?
Thanks






RE: How to widen existing footing
If this doesn't work, you could expose the ends of the rebars in the footing, and connect rebars to them with mechanical splices. Then add additional footing as required.
DaveAtkins
RE: How to widen existing footing
That was 10+ years ago and the solution was really my bosses suggestion (he was the EOR). Hence, my memory isn't all that clear about it. But, I don't recall experiencing any major problems with the solution. In fact, I remember the field being pleased with the relatively simple solution.
RE: How to widen existing footing
RE: How to widen existing footing
I don't understand your recommendation. The footing is usually designed to accomodate the column moment. It seems you are suggesting the other way around. Can you elaborate?
I don't have the flexibilty of mechanical splice connectors.
Josh,
I don't fancy extending the footing by epoxying into the side of it. Getting the tension to tranfer across the epoxied joint and into the existing bars seems cumbersome and really like a hit or miss.
Any other thoughts?
RE: How to widen existing footing
RE: How to widen existing footing
Chemical anchorage may be fine, if you carefully select the product for the exposure and continuous loading.
RE: How to widen existing footing
I'm in a remote country and mechnical connectors are simply no available.
RE: How to widen existing footing
As you have been hired by the contractor, what does the responsible design engineer for the project say about this? It is ultimately his responsibility to approve any solution.
RE: How to widen existing footing
I recently did the same for a footing that was poured in the wrong place and it didn't work as the contractor placed it.
RE: How to widen existing footing
I understand the transfer of shear and moment across the joint but what happens across the joint. Do you simply apply the loads to the old section? Can the tension effectively get back into the existing bars? Is there a spacing requirement between the new dowel and existing steel? If we were doing a lap splice then there would be lap lenght requirements and spacing limitations unless it was a mechanical splice. Drilling more than 6-8 inches is probably not practical.
RE: How to widen existing footing
Regarding my other solution, tclat, draw a free body diagram of the column and footing. Apply a uniform bearing pressure under the footing, equal to the vertical load in the column. The eccentricity between the centroid of the bearing pressure and the center of the column creates a moment that must be resisted by the column.
DaveAtkins
RE: How to widen existing footing
Even if the column can resist the moment strengthwise, you are neglecting the flexibility of the column. It will bend, and the vertical load from the column will go straight down.
I agree that epoxied bars are not an appropriate solution for the bending.
RE: How to widen existing footing
Determine the actual bearing stress and use that to find the moment at, say 1'-0" from the joint. I check to see if 9" of development is enough for the amount of steel I have compared to what I need. If it is, I provide a 1' embedment (of the bottom bars only) in an epoxy. If it's not enough, I'll try 1'-4", and so on, until it works. You'll get a longer embedment on the bottom bars. I also provide top bar dowels (even if there are no top bars in the footing) just to help with shear transfer. I only use the embedment needed for development of Fu at the top.
RE: How to widen existing footing
BA
RE: How to widen existing footing
www.PeirceEngineering.com
RE: How to widen existing footing
What about a few helical piers/anchors driven right along side of the footing. The footing is then held up, from below, by one of their canti. brackets off the pier stem?
RE: How to widen existing footing
RE: How to widen existing footing
RE: How to widen existing footing
I decided to go with the option I noted above.
This is a design build project so I am also the design eng.
Mobilising a crane or rig for doing any type of piling is a bit much for one footing in a remote site. The contractor definitely would prefer not to drill more than 6 inches
I would have probably gone with BARetired's option if the floor was already in place since it would be better if the footing bars were continuous through the column as opposed to just epoxied 6" on each of the four faces. Couldn't wait since the client wanted things rectified before we moved on.
RE: How to widen existing footing
You could demo the footing back and provide a welded splice. This could bring the lap length back to 6-8".
RE: How to widen existing footing
The tricky thing I nearly forgot is: you have to size the new footing build-out (in plan view) for the NEW load. In other words: treat the existing footing like it already sees the DL+LL on a day to day basis. Then size the new (combined) footing so that the increase is not driving the bearing pressure of the old footprint too high [i.e. you will superimpose the pressure from the load addition (with the new plan dimensions) on the old pressure]. It will result in low pressure for the new [exterior] footprint....but I still designed the new concrete so that it could see the almost all the load in case the LL was not in place at the time the modification was made.
You need room to do it....but it can work if your existing concrete is good enough to anchor to on top (and on the pedestal).
My thoughts.
RE: How to widen existing footing
If the footing is a gravity footing what load does it see other than LL and DL? I would suggest that if the building is still under construction (as is usually the case when this kind of contractor error is discovered) that there is no LL on the footing and likely a small % of DL.
It is definitely something to think about though/
RE: How to widen existing footing
The reason for my modification was not contractor error: it was an existing footing that was going to pick up about 30 extra kips from some new equipment. The icing on the cake (that help prompt my solution) was the fact that the concrete at the bottom of the footing made attachment questionable.
It was a tough problem but things turned out ok.......never got a phone call.