Fire Pump Grouting

Fire Pump Grouting

Fire Pump Grouting

(OP)
I have a fire pump and since the GC was going to pour more concrete, we set the pump up on 3/4" A. T. Rod with 1" sch 80 pipe nipples (sleeved the Rod) and they formed and poured the pump pad, my question is; the lower lip of the pump base is encased in the concrete so where does the NFPA 20 requirement come into play for grouting?

spkreng, CET

RE: Fire Pump Grouting

If I recalled correctly I had the same question while taking a NICET test.
The answer I found was that the entire based must be in contact with the concrete and the entire based must be filled with concrete as well. No empty pockets allowed.

RE: Fire Pump Grouting

I agree with NJ1. The last ten pumps I installed, the pad was formed all the way up to the bottom of the base plate which would fulfill your grouting requirement.

If we all agreed, we would be Communists.- Me.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources