Does anyone have any information on the construction of 115/230/500 kV electricity pylons? I would like to know whether or not every pylon along a circuit typically has its own ground grid. Also what are the design details (such as arrangement/dimensions of conductors) for typical ground grids used for electricity pylons in this class? Thanks.

RE: 115, 230, 500 kV transmission tower construction

What do you mean by 'pylon'? 'Structure', as you have in the title of your post?

You appear to be asking more about the DESIGN of a tower, than its construction, which is how it is put together.
Is the structure you are building wood, or steel?

Practice likely varies by utility, but for us, we have minimum ground impedance that must be met at each tower. If a grounding study indicates the ground is poor, we may install ground rods, counterpoise, or take other measures to reduce the ground impedance to a suitable level.  

RE: 115, 230, 500 kV transmission tower construction

If you tie the anchor bolts to the rebar, the foundation may be an adequate ground by itself.  This is what is called a "Ufer" ground.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources