ASME B31.1 - 319.4 Flexibility Analysis
thread292-246231: B31.3 Thermal stresses
I am not sure whether I have determined the correct anchor distance U in my calculations to check the requirement for Flexibility Analysis as per 319.4.
Question: In determining U (straight line distance from anchor to anchor), does it mean the diagonal distance between anchors in a rolling pipe?
What I did is use the simple space phytagorian (c2 = a2+b2+h2) to calculate the distance. Can anyone tell me if my procedure is correct?
Thanks in advance.
RE: ASME B31.1 - 319.4 Flexibility Analysis
What are your X,Y and Z projections?
The projections between two anchors being considered are:
x=2363 mm
y=3226 mm
z=1488 mm
This comes out after algebraically adding all the piping segments on the pipe spool roll being considered, done for each corresponding axis.
I simply assumed that U = SQRT(x^2+y^2+z^2)= 4227 mm
To be use on Flexibility Analysis check through equation (16) in 319.4.1.
Any comment on this?
You are correct but note the limitations of the simple check especially the fact there should be no supports/restraints!!!
Thanks DSB123, appreciated.