HSS Column with conc force

HSS Column with conc force

(OP)
I have a question(s) concerning applied axial forces to an HSS column connection, given:
HSS 8x8x5/16 with W14 beam framing into it.
axial load is 5k
vert reaction 25k
moment is 50 k-ft

part twelve of the manual page 12-26 says the WT tees should be long enough to use flare welds at the corners of the HSS.
if this detail is used do you still have to check the conc force applied to the HSS at top and bottom flange with spec K1,4  and equation K1-9?
If you used this equation 1-tp/B = 0???? because tp = B

in the manual companion, examples spec K, AISC mentions that it is ok to use shorter WT and fillet weld to the flat of the HSS column - as long as you meet the criteria given by K1-9, correct?
given an HSS with less than tf of 1/2" this can really limit the connection, would this problem then be solved with column cladding shown on 12-28?

which connection method is most commonly used (flare weld to the corners or fillet weld to the flat)?

thanks in advance for any advice.

RE: HSS Column with conc force

You can use a built WT (2 plates).  With a 9" connection, fillets may work best.  The flare bevel (BTC-P10) is limit to an effective strength of 5/8xwall thickness (3/16).  The WT flange must be thick enough to not put the fillet welds in prying.    

Other options are a single through plate or flange plates for the moment and axial with a shear tab in the web.       

http://www.FerrellEngineering.com

RE: HSS Column with conc force

(OP)
a prelimanry finding came up with a pretty heavy WT section, had Bf = 11 in and thicknesses at max allowable by a 1/4 weld to the 5/16 HSS wall. if i use a shear tab as well may have to notch out the WT flange.

 

RE: HSS Column with conc force

rnorth
I don't understand your shear tab and notched WT comment.  

If you require an excessively large WT, it is probably best to make the WT out of two plates.  Why are you not connecting the beam flanges for the moment?    

http://www.FerrellEngineering.com

RE: HSS Column with conc force

(OP)
the beam flanges area connected to the HSS with the WT's top and bottom flange to transfer the flange forces to the HSS column.

the shear carried by the beam is taken thru a shaer plate connector bolted to the web

RE: HSS Column with conc force

Ahhhh.  No I see, I think. I have never seen WT's used as flange plates.  Why not just plates?  I will attach a sketch.  

http://www.FerrellEngineering.com

RE: HSS Column with conc force

(OP)
thanks, what is your take on AISC eqn K1-9, if the plate or WT is longer than than the HSS width this limit no longer applies?

 

RE: HSS Column with conc force

(OP)
thnkas for the sketch

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close