pedestrian bridge vibration analysis

pedestrian bridge vibration analysis

pedestrian bridge vibration analysis

(OP)
I´m designing a cable stayed pedestrian bridge in Spain. It´s not specified in Spanish codes the analysis for vibrations due to pedestrian walk through.
Is there an specific European code where this is stablished?
Which is the method used in the US?
 

RE: pedestrian bridge vibration analysis

In the US
GUIDE SPECIFICATIONS FOR DESIGN OF PEDESTRIAN BRIDGES published by AASHTO

In general you estimate the fundamental frequency as a simply supported beam.

Download the SPECOM specification from Contineal Bridge.  They show a worked out example of a truss bridge.

 http://www.continentalbridge.com/assets/pdf/intro.pdf

I generally model the bridge using Finite Elements and compare with a simply supported beam as a sanity check.

As far as Europe specification I don't know, If you find some I would be interested.

RE: pedestrian bridge vibration analysis

(OP)
I´m using sap2000,
let's check the procedure to see if it is ok:

1. Sap2000 finds the lowest frecuency mode
2. I calculate the fundamental frecuency as simply supported beam to check sap2000 results
3. The AASHTO Pedestrian Bridge Guide stablishes that the fundamental frecuency should be greater than

f>=2.86*ln(180/W)

where W is the wight of the bridge in kips

Questions:

a. W includes the whole live load mass?
b. I guess worst situation is when W is lowest (no live load mass)?
c. The AASHTO equation does not take into account type of bridge (cable stayed), span length. !?

No Eurocode on the affair so far.

RE: pedestrian bridge vibration analysis

(OP)
I´m using sap2000,
let's check the procedure to see if it is ok:

1. Sap2000 finds the lowest frecuency mode
2. I calculate the fundamental frecuency as simply supported beam to check sap2000 results
3. The AASHTO Pedestrian Bridge Guide stablishes that the fundamental frecuency should be greater than

f>=2.86*ln(180/W)

where W is the wight of the bridge in kips

Questions:

a. W includes the whole live load mass?
b. I guess worst situation is when W is lowest (no live load mass)?
c. The AASHTO equation does not take into account type of bridge (cable stayed), span length. !?

No Eurocode on the affair so far.

RE: pedestrian bridge vibration analysis


I am working on 3 large pedestrian bridges over the Las Vegas strip.  In looking at AASHTO, you'll find that the frequency limit is a form of equation 4.1 from the AISC "Floor Vibrations Due to Human Activity", by Allen and Murray.  I would be cautious in applying the AASHTO formula directly, as it assumes only one person weighing 157 pounds to be walking on the bridge.  If you are expecting dancing or rythmic excitation, you will have more problems.  I would recommend looking at the AISC publication.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources