Has anybody ever used one this size at 480V.  I am wanting to use a 6000A circuit breaker as my cross tie between (2) 2500kVA transformers on each side and was told they don't make them that big.

RE: 6000A circuit breaker at 480V LVPCB

It's unusual, but available.  Can't comment on your design needs or choices.

Rafiq Bulsara
http://www.srengineersct.com

RE: 6000A circuit breaker at 480V LVPCB

Yes they do, I have a few of them in stock, ABB, GE, and some old Westinghouse ones.

However, you may wan't to rethink your idea. That is a lot of fault current you are proposing.  

RE: 6000A circuit breaker at 480V LVPCB

2.5MVA Xmer with LV secondary is like skimming the limits..both operating current and short ckt current will be difficult to address.

RE: 6000A circuit breaker at 480V LVPCB

(OP)
That's exactly where I am at right now with the client.  Is it a decent idea to lower the transformer kva (1500) and utlize fans and pumps to increase the kVA.  Because the fault current will be base upon the self cooled level of the transformers.

RE: 6000A circuit breaker at 480V LVPCB

Guess I am a little confused here, if the application is a tie breaker why do you need 6000A? The tie should be the same size as the mains are. Add key interlocks and you won't have to worry about fault currents either.

Maybe I am just thinking wrong, perhaps a sketch would help.  

RE: 6000A circuit breaker at 480V LVPCB

My rule of thumb has been that for anything over 4000A you're looking at the wrong voltage.

RE: 6000A circuit breaker at 480V LVPCB

3000A on Mains and tie is sufficient. Where are u getting 6000A?

"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic — and this we know it is, for certain — then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". – Nikola Tesla
 

RE: 6000A circuit breaker at 480V LVPCB

(OP)
So they can sync with eachother.  2500/480*1.732 = 3000A's x2 = 6000A's

RE: 6000A circuit breaker at 480V LVPCB

(OP)
Medium voltage is not an option.  Even though it is the correct answer.

RE: 6000A circuit breaker at 480V LVPCB

You're building a maintenance department's nightmare.

FWIW, at a previous employer we had a number of boards fed from 2.5MVA transformers with 4000A incomers at 415V. We struggled to get a board with adequate fault bracing to allow paralleled operation, and the arc energy was approaching 200 Cal/cm2 when on a single feed (slow protection to coordinate with some big stuff downstream). At that energy level the question is whether the clean-up guys will need a vacuum cleaner or just a dustpan & brush to collect you, not whether you'll be alive or not.

Have you any option to split into two boards with smaller transformers?
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: 6000A circuit breaker at 480V LVPCB

Why x2?

RE: 6000A circuit breaker at 480V LVPCB

(OP)
x2 because if they ever want to kill one side but not the xfmr's.  They don't ever want to be on just one utility circuit.  How the building is now.  Arc flash and fault current are another issue that I am trying to deal with as well.  This is my 3rd VERY large client that is getting rid of all the medium voltage no matter what it takes/costs.

RE: 6000A circuit breaker at 480V LVPCB

But the tie will never have to carry the load of two transformers, always only one.  There is no need for the tie to be larger than the mains.

RE: 6000A circuit breaker at 480V LVPCB

From the diagram it looks like you are referring to the 6000A breaker that is serviced by two 2500 kVA transformers on either side?  So you have 5000 KVA worth of transformer on either side of the tie.  May I ask how you are dealing with the 152kA worth of short circuit current?

------------------------------------------------------------------------
If it is broken, fix it.  If it isn't broken, I'll soon fix that.

RE: 6000A circuit breaker at 480V LVPCB

Oops, I hadn't looked at the one-line, thought M-T-M and wrote away.  The one-line is a disaster waiting to happen.

Why not a ring bus with two of the breakers open and the rest closed, something like:

CODE

      |               |               |               |
      |               |               |               |
<-[x]---[x]-------[x]---[o]-------[x]---[x]-------[x]---[o]------>
            |   |           |   |           |   |           |   |
            |   |           |   |           |   |           |   |
           [ ] [ ]         [ ] [ ]         [ ] [ ]         [ ] [ ]

That version adds in a few extra, but purchasable, breakers.  A 12 breaker ring would save a breaker or two.  Have an interlock scheme that never allows more than two transformers on any bus segment at once and you're good to go.  Except you're still at the wrong voltage level.

RE: 6000A circuit breaker at 480V LVPCB

That one line sure clears a lot up, I was also thinking M-T-M like DB was.  

RE: 6000A circuit breaker at 480V LVPCB

This is way too much for one board. You really should consider splitting the load some how.

Are the utility circuits synchronized? Is the utility aware that you want to parallel their circuits on the secondaries? Most would not allow that.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: 6000A circuit breaker at 480V LVPCB

(OP)
I was going to deal with the 152kA of fault current by installing a 200kAIC board.  I was also looking at the cutler hammer current limiting fuseless circuit breakers.  The utility is aware that we are sync'n their circuits and are ok with it.

Also to deal with the arc flash problem - I was going to install a maintenance switch and make it so nobody unauthorized would be allowed in the room and tie the door contacts and motion sensor into that.

At the end of the day I just want to deliver a safe system to my client.  They already had everything worked out for me before I got there, so just trying to chizzle it back one thing at a time.

David - I really like your setup and I pitched that on day 1, but they said they want all 4 transformers supplying load at the same time.  But I am going to fight the good fight.

RE: 6000A circuit breaker at 480V LVPCB

Have you found an ATS that can handle the fault current, or are you planning to add fuse protection?

The Cutler-Hammer breakers may not coordinate above 100kA, if that's a concern.
 

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: 6000A circuit breaker at 480V LVPCB

IS this a primary or secondary service? How about some Metal Enclosed Switchgear with interlocks and ties on the primary side?  

"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic — and this we know it is, for certain — then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". – Nikola Tesla
 

RE: 6000A circuit breaker at 480V LVPCB

I have another question: Why is the bus tie necessary?  Could you simply put an extra transformer in the system with a breaker going to each bus in place of the tie?  This way you could switch on the 5th transformer in the event you need extra power on one of the buses and not worry about ever connecting them.  Granted, not the cheapest solution, but perhaps less maintenance.  You could also spec this transformer to have a higher impedance and possibly a lower KVA rating which would lower your fault currents significantly.

I also like davidbeach's suggestion.

------------------------------------------------------------------------
If it is broken, fix it.  If it isn't broken, I'll soon fix that.

RE: 6000A circuit breaker at 480V LVPCB

(OP)
Great idea turbineGen - I like that one.  Eliminate the tie breaker and put a transformer in the middle that swings both ways.  This will be a secondary service with metal clad gear.   

RE: 6000A circuit breaker at 480V LVPCB

Just be sure to interlock the breakers or you could end up creating a bus tie and be right back where you started.  The nice tyhing about a switchable spare is it allows for more load in the future as well.

------------------------------------------------------------------------
If it is broken, fix it.  If it isn't broken, I'll soon fix that.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources