Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"Because of this forum, I continue to WOW! my clients!"

Geography

Where in the world do Eng-Tips members come from?
mcgyvr (Mechanical)
19 May 10 11:10
This just doesn't seem right to me and wanted to see what others think. We use a product (DC fuse panel) with a bus rating of 100A. Per UL we need to protect it with a max. 125A overcurrent device. However they only thermal test that product to the bus rating of 100A. With a 125A overcurrent device that product could hum along for ever at 125A without the overcurrent device ever tripping.

I would think that you should protect it with an overcurrent device no greater than your bus rating. So bus rating = 100A, overcurrent device = 100A. Is this yet another hole in the standards that hasn't been plugged?
DRWeig (Electrical)
19 May 10 11:48
mcgyvr, is this under UL 508 or UL 508A, or another standard?

DW
mcgyvr (Mechanical)
19 May 10 11:49
For example (see general specifications..Electrical) http://www.telect.com/www/Products/LearnMore.aspx?CatalogId=Telect+Products&ProductId=Low-Current+GMT+Fuse+Panels_pid1137&VariantId=HPGMT10

I have a feeling this is just incorrect and that it should be a 100A bus rating, a 100A interupt device with the wiring sized to 125A.
mcgyvr (Mechanical)
19 May 10 11:49
UL 60950
DRWeig (Electrical)
19 May 10 11:57
Rats, that standard isn't in my library, so I can't see it in context.

Could it be that there's an allowance for loads that have inrush current (capacitive things I guess)?  Same way we protect motor circuit conductors with overcurrent protection set higher than listed ampacity.

I can see how that might be needed.  Each circuit coming off your bus has its own fuse protection, so if properly designed it might be OK.

Personally, I'd put a 100% protector on it (or less, depending on my loads)...  The 125% is a maximum after all.

Anyway, I'm just thinking while typing --

Anybody else out there?

Good on ya,

Goober Dave
mcgyvr (Mechanical)
19 May 10 12:09
Yes each circuit has its own fuse. This usually feeds only resistive loads. The product is basically a large input connection which feeds multiple fuses that provide protection to multiple pieces of equipment. Just like any other fuse/breaker panel in your house,etc... It just bothers me that the products are only tested by UL to 100A but then allowed to be fused at 125% so the panel could be running over its tested rating for an indefinite time which can easily create a fire hazard,etc... Then it is also recommended to use a 2 AWG wire to feed the panel which is only rated to 115A per NEC 310.16 75 deg C column.

It just doesn't seem right.
mcgyvr (Mechanical)
19 May 10 12:43
I guess this comes from requirements to size overcurrent device at 125% of the continuous rating. So the continuous rating of that panel is 100A. But I would still think UL should test the product to 125A since it "could' run at 125A for an extended period with a 100% rated overcurrent device. 125A is worst case scenario and not 100A.. Just another hole in the testing/safety world IMO
SteveSmith (Mechanical)
19 May 10 13:45
mcgyvr,

You have to remember that UL comes in thinking about fire safety 1st and above all other concerns.  Electrical safety, while important is a second class citizen.  I've worked with UL on products under UL 1778, 60950, & 508A and it's always the same.  I belive if you check the NEC standards (again a fire safety standard), you'll see the 125% is pretty common.

Steve Smith

DRWeig (Electrical)
19 May 10 13:52
I would still agree with McGyver that UL's bus rating process should include extended-time overcurrent at 125% of what they're ultimately going to rate it.  

You should see the tests they do for small transformers, it's a hoot.  

Goober Dave
SteveSmith (Mechanical)
19 May 10 14:00
I also agree that you would expect them to test the product at the 125%, but I have never seen it happen.  As long as the fuse/breaker trips during a dead short they seem to be happy.

No thanks on the transformer test.  I've had my fill with UPS, Power Factor Correction equipment, & UL 924 Emergeny Power Systems.

Steve Smith

mcgyvr (Mechanical)
19 May 10 14:01
oh well..can't change the world, but I can make my little piece of it safer.. Panel will have overcurrent device rated at 100A.
Thanks guys...
 
 
dpc (Electrical)
25 May 10 10:50
Just keep in mind that a 100 A molded case circuit breaker is only rated to carry 80 A on a continuous basis, "continuous" being defined as three hours or more.  Beyond that, it may trip.  

So your 100 A bus is now only good for 80 A on a continuous basis.  

 

David Castor
www.cvoes.com

mcgyvr (Mechanical)
25 May 10 10:57
The ones I'm using are rated to carry 100% continuous. But yes I am aware of that on other models. Thanks.  

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close