When supply and return fans are starting, recircule, fresh air and exhaust dampers are open or closed, which is right?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
fan start damper position
|
fan start damper positionfan start damper position(OP)
When supply and return fans are starting, recircule, fresh air and exhaust dampers are open or closed, which is right?
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesThe world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
Engineering-centric businesses face a number of challenges today, but unmanageable design and change processes don’t need to be counted among them. Download Now
|
RE: fan start damper position
The Control system energizes when the fans are turned on
The MA temperature is maintained by modulating mixing dampers.
OA and EA dampers close and RA damper opens when fan is off, and modulate for MA temperature Setpoint control when fan is on.
There is a damper control and setpoint for minimum ventilation damper position when MA temperature is satisfied
NOTE: This is not 22% OA or OA damper open 22%, it is the control program output value necessary to position the OA damper such that the design OA cfm is maintained to provide a healthy CO2 level in the building
Features
1. The proper proportions of OA and RA are admitted to prevent the MA temperature from dropping below the desired MA temperature.
2. A minimum quantity of OA, determined by the setting of the minimum position switch is assured at all times.
RE: fan start damper position
But, I mean only starting position, not normal operation.
When supply and return fans begin to start, high current occurs. to prevent the fan motors, some consultants advice closed damper starting, others advice open damper starting. Please, declare your opinion.
Thanks.
RE: fan start damper position
I believe this is because of the more dense cold air causing motors to trip on the higher load.
RE: fan start damper position
RE: fan start damper position
RE: fan start damper position
Sounds like exactly what you said, but stated a different way. OA damper won't open up after freezstat until after warm-up. Just a lot of variations by AHU and application. If a relative negative environment, you reverse the proof of flow (dP and CT) from supply side to exhaust side. If the heating or cooling coil is included, you modulate the valve to meet MA discharge. If you have separate minimum OA and economizer, well, ad nauseum.
First step I usually look at is after control circuit is energized, motors are locked out until smoke control dampers meet end switch. I like having proof of flow as well as end switch, but different designers do different things.
No one-size fits all answer, but I've never encountered change in air density being a factor on start up draw.
RE: fan start damper position
You are quite right that's why I said " A Typical Mixed Air Control" because there are many varations so I didn't want to get too technical but tried to focus on the mixing dampers. All we can do is try as best we can to help :>)
RE: fan start damper position
Closed dampers = less airflow = lower motor current at start up.
For across-the-line starts at any rate. Less important if the fan is driven via VFD and has soft-start.