PVC selction for POWER CABLES
PVC selction for POWER CABLES
(OP)
how we can select PVC material for PVC insulation and PVC sheath if we need properties a)all at a time or b)in combinations such as for particular cable,
fire retardant
fire resistant
oil resistant
anti termite
anti rodent
low smoke
low helogen
Is there any particular criteria for selection???
fire retardant
fire resistant
oil resistant
anti termite
anti rodent
low smoke
low helogen
Is there any particular criteria for selection???






RE: PVC selction for POWER CABLES
You cannot have both zero halagon and FR with PVC oter sheath.Since there are lot of similar products in the market,best method is to get a set catalogues and find out the best product suits your application.
RE: PVC selction for POWER CABLES
PVC cannot be low smoke and halogen free as the resin it self contains chlorine. For insulation one could take XLPE or for low voltage even PUR [it is oil resistant too].
For jacket, ethylene/vinyl acetate (EVA) highly doped with aluminum oxide will be low smoke and fire retardant [but will be not indicated to pull it through conduits or duct].
Armored cable is good anti-rodent. Fire resistant could be mineral insulated or glass fiber insulated. Anti-termite are chemicals added in the jacket material.
RE: PVC selction for POWER CABLES
------------------------------------------------------------------------
If it is broken, fix it. If it isn't broken, I'll soon fix that.