Hi,
    During my work, I need to adjust one time-coefficient(1m20s--1m50s) on the PLC for control use.  But as I download the modified data to PLC,the system shows "not enough load memory space'.I check the working memory . it is about 94% used. But What confused me more is that I only modify one coefficient.Why cause this problems(occupy such big memory?). I need your help to settle this problem but not cost extra money to buy a lager memory.Would u help me .Thanks for your time and attention  
linlin
From China

RE: urgent problems on siemens SIMATIC S7-300/400

just a thought, is there some memory that is dedicated or reserved?  Also, in binary is going to 1m50s requiring an additional byte of memory?

wbd

RE: urgent problems on siemens SIMATIC S7-300/400

Just a thought, but you might need to compress the memory. To do this under Simatic Manager go to PLC,then from the drop down menu choose Module Information. Choose the memory tab and there is a button to compress the memory. I have had this problem before when there was plenty of free memory. I just needed to use this compress memory function.
Maybe you are having the same problem. Hope this helps.

RE: urgent problems on siemens SIMATIC S7-300/400

With memory that full you must delete the bolck you are trying to replace! If the process can not stop delete OB1 first (Iam assuming your Block is being called by OB1.) Then delte your Block Being replaced. From the off line manager select your new block then OB1 and download.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources