Helo guys.

I would like to ask one simple question.

i have a network of water being pump through a single pipeline.

By calculation, the total discharge head of my pump is 6.6 bar.

At the same time, the pressure gage on the pump outlet on site is showing a value of 6.5 bar.

Does my total discharge head by calculation is referring to pressure gage reading?

Please check the attached picture for clarification.

thank you

 

RE: total discharge head = pressure gage reading?

That just means the pressure being exerted at the discharge of your pump is 6.6 bar, and at the guage, the pressure being exerted by the fluid is 6.5 bar. In an ideal situation, the two would match.

"Scientists dream about doing great things. Engineers do them." -James Michener

RE: total discharge head = pressure gage reading?

You are using the words "total discharge head" which is a valid term.  Are you using total discharge head as the full word version the acronym TDH?

If so, TDH can also indicate total dynamic head which refers only to the the head rise across the pump, so in that case, to obtain total discharge head (gage reading) you would have to either add or subtract - whichever is the case - the suction pressure at the inlet of the pump.

Could this be what is squirreling up your numbers?

rmw

 

RE: total discharge head = pressure gage reading?

Total_Discharge_Head =
Suction_head +
Suction Velocity Head +
Pump_Differential_Head +
Discharge Velocity Head


From www.pumpfundamentals.com

It is common to ignore the velocity heads.  They are usually not very high values.  Your pressure gage won't read the velocity head components anyway.
 

**********************
"The problem isn't finding the solution, its trying to get to the real question." BigInch
http://virtualpipeline.spaces.live.com/

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources