What width of ope is possible in an existing 200 thk prestressed concrete slab spanning 6.1m approx 1.2m wide.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Placing opes in prestressed hollowcore slabs
|
RE: Placing opes in prestressed hollowcore slabs
1. If you know the slab's manufacturer, ask them. Sometimes they will cut the hole for you for a fee.
2. Do the slabs have a grouted key along their adjacent sides? If so, this greatly simplifies things, since the key will transfer load along that joint.
3. Will the size hole you want mean cutting the prestressing strand? Will it mean cutting one slab completely across or will the hole span part of two slabs?
4. If you cut the slab completely across its width, you will need a steel "hanger" to carry the two sides of the cut slab. The manufacturer has standard details for these.
5. Don't forget to shore the slab from below BEFORE cutting to support the ends while you install the hanger.