top chord joist extensions - typical support condition
I have the condition where Type "R" joist extensions for K series joists have an extended span of roughly 4'-0".
Are tabulated load tables typically based on a simple span or a cantilevered span?  I need to know if the closure piece that I am putting at the "free" end should be designed as load-bearing.  Specifically, I am looking at Vulcraft joists.
Thanks.
RE: top chord joist extensions - typical support condition
Generally for the simple support span distance and the joist end is reinforced for the cantilever... That long a cantilever can be a specialty item and the tables should be used for as a guide only.
Dik
Agreed...
Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask
I should clarify that I am looking at the "Top Chord Extension Load Table (R Type)" which tabulates top chord joist extensions of up to 6'-0".
The Vulcraft representative just got back to me - he said that the values in the "Top Chord Extension Load Table" are for a cantilevered support condition.  Deflection must be independantly checked using the tabulated section modulus and moment of inertia.
Thank you for replying to my post.