Footing Punching Shear Reinforcement

Footing Punching Shear Reinforcement

Footing Punching Shear Reinforcement

(OP)
I have an EXISTING 24"sq concrete column bearing on a 10ft sq footing, 30" thick, f'c=6ksi.  

i am adding several stories above this footing on top of the existing 4 story structure, but i am limited by the punching shear capacity of the footing.

i wondered if anyone has any ideas to reinforce the footing for punching shear.  i think that thicknening the footing with a composite topping wont work because the bearing stresses will still be founded below the new topping.

im trying to avoid shoring up the column and collaring on a new column "wrap" to increase bo.

any ideas?

RE: Footing Punching Shear Reinforcement

What about bolting on a steel collar to the column and bearing onto the footing, to increase the shera perimeter.

Otherwise, 'collaring on a new column "wrap"' seems feasible, but why would you have to shore up the column to do this? (BTW I don't know what 'bo' is)

RE: Footing Punching Shear Reinforcement

None of us know what "bo" is, so why are we responding to this thread?  Reinforcing the footing for punching shear is not a problem, so what, exactly is Galambos getting at?

BA

RE: Footing Punching Shear Reinforcement

Quote:

None of us know what "bo" is

bo = body odor

You're welcome.

RE: Footing Punching Shear Reinforcement

Notwithstanding the clever remarks of abusementpark, what exactly is the problem?  Reinforcing for shear is not usually a problem.  Perhaps abusementpark can elucidate a bit further on what he perceives to be the problem.

BA

RE: Footing Punching Shear Reinforcement

Or, perhaps Galambos could expand on his initial question.  I don't see the problem.

BA

RE: Footing Punching Shear Reinforcement

bo is the perimeter along the critical section as defined in ACI for punching shear (it is directly in the formulas for punching shear).  bo is based on the width of the column and the depth of the footing as defined in ACI.

It sounds like he needs bo to be larger to make the punching shear work.

RE: Footing Punching Shear Reinforcement

So "bo" is actually b0, right?

BA

RE: Footing Punching Shear Reinforcement

(OP)
BAretired's brash responses never cease to amaze me. Wow.  Perhaps, if you dont see the problem, you have no business responding to the thread, or at least keep your opinions to yourself and act like a professional.

Kudos to abusementpark for explaining bo or b0.  Collaring onto a steel column may work although I have about 1000 kips to transfer into it.

As for shoring, my intent was to relieve load on the footing to install the repair, although, I can see the collar working without shoring.

RE: Footing Punching Shear Reinforcement

I would look at the steel bracket collar idea first.  I'd also have to question whether the soil bearing pressure is OK with all those additional stories added.  Wouldn't there be a limit to the bearing pressure?

One other idea that I thought of is what I did on an old steel fabrication plant once, where the spread footings were inadequate.  We drilled holes through the footing vertically - around the column - and drilled in auger cast piling.  The tops of the piling were mushroomed out directly beneath the existing footing to serve as a sort of in-ground capital to engage the existing footing.  

For your case, the added piling would increase footing capacity (in terms of the soil) and also perhaps negate the shear issue since you could probably get the piling close enough to the column where shear wouldn't matter.

 

RE: Footing Punching Shear Reinforcement

i am not familiar with the "collar" approach although I can imagine what it is.
Does anyone care to elaborate?

Thanks.

RE: Footing Punching Shear Reinforcement

i knew what he meant by bo.

RE: Footing Punching Shear Reinforcement

...not everyone uses the ACI code in this forum

RE: Footing Punching Shear Reinforcement

I also know what bo is.

You could use gunite to increase the column size if that would help. If you are adding several stories it would seem that there would be more questions than punching shear in the footing.

RE: Footing Punching Shear Reinforcement

Sorry Galambos.  I apologize.  I should have put 'b' and 'o' together.

BA

RE: Footing Punching Shear Reinforcement

I do not mean to derail the thread, but I too would like to pose a question about punching shear for a spread footing:

In the Canadian Code, if the face of the column is less than 5 x d from the edge of the slab, then that face shall not be effective in resisting punching shear.

However, for foundations, more often than not, the pier is less than 5 x d from all edges of the spread footing. Does this automatically rule out punching shear from governing or should I check for punching shear assuming all faces are effective?

Clansman

If a builder has built a house for a man and has not made his work sound, and the house which he has built has fallen down and so caused the death of the householder, that builder shall be put to death." Code of Hammurabi, c.2040 B.C.

RE: Footing Punching Shear Reinforcement

Always check punching...because it is a rather simple check, if for no other reason.  

RE: Footing Punching Shear Reinforcement

(OP)
BA, apology accepted.

Yes, punching shear is not the only issue, although I have repairs in mind for the underreinforced footing and soil bearing issue.  

I suppose I would need shrink reducing agent in my mix, if I were to use a concrete collar.  Also, I'm curious if the adhesive anchors would relax to much during loading that would make the collar (steel or concrete) ineffective.  Perhaps, the movement is negligible.

Thoughts?

RE: Footing Punching Shear Reinforcement

I'm not sure about a shrink reducing agent.  If the collar shrinks, it wraps more tightly around the existing column thereby improving bond.

I would think roughening the contact surface would be a good idea as well as headed studs epoxied into the column.  

BA

RE: Footing Punching Shear Reinforcement

How much do you need to increase the bo?  I would feel more comfortable with a steel collar, but transferring 1000 kips is a lot for mechanical fasteners.

Did you test for the concrete strength?  6 ksi is a lot for a foundation.

 

RE: Footing Punching Shear Reinforcement

You could drill sloping holes into the footing all around the column into the truncated pyramid describing the punching shear failure surface under the column.  You could then epoxy reinforcing bars in the holes with the top projecting up and away from the column.  

A concrete collar, say 4'-0 x 4'-0 in plan would then totally enclose the sloping bars.  The vertical component would assist in carrying the column load.  The horizontal component would tend to improve the bond between collar and column.

Such bars would need to be totally developed below the punching shear failure surface.
 

BA

RE: Footing Punching Shear Reinforcement

Are you also going to increase the rebar area of the foundation due to additional loads?

(Just curious, if it's irrelevant please feel free not to answer...thanks)

RE: Footing Punching Shear Reinforcement

using ACI...if you say your "d"=27"....then bo is 312"....that would result in over 2200 kips....I think you might have issues with the 10x10 footing unless your on somethin really really stiff

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources