Trip coil supervision

Trip coil supervision

Trip coil supervision

(OP)
I saw a 132kV capacitor beaker with three individual pole operating mecanism.
obiviously the breaker has three separate individual trip coil for three poles.
Now for supervison of trip coils, In my opinion, we need three separete coil relay (could be a one reay with three coils)
I saw single coil supervision relay in the circuit for supervision of three trip coils that are in parallel.

I believe the circuit is not good.

Do anyone have experience of supervising three parallel trip coils with one coil relay.



Thanks in advance for advice.

Pukar

RE: Trip coil supervision

Some trip coil supervison devices monitor the milliamp current to the trip coils with enough accuracy to detect the difference between 2 or 3 coils in parallel.

Some relays can be specified with several trip output contacts with built-in coil monitoring so single pole tripping and monitoring are possible. Most relay designs still look for a single trip coil.

Other systems depend on the pole diagreement alarm to alert the operator action or initiate a breker failure action.

In my limited experience, the primary cause of trip coil failure was loss of trip circuit power.  A single monitor will alarm for this condition.

The expense and complication of monitoring three coils oer breaker createw a lot of complexity which can lead to reduced reliability.  Except for very critical circuts, the added benefit is not worth the cost and complexity.
 

RE: Trip coil supervision

(OP)
RC wilson,

Thank you for the nice explanation.


Pukar

RE: Trip coil supervision

Hi.
We use one TCS per coil.
Possible use a one device for the 3 coils, for example TSG 930: http://www.seags.ch/ses/tsg/.
 Importnat point: monitoring of trip coil of openeed CB

Good Luck
Slava
 

RE: Trip coil supervision

Quote:

Importnat point: monitoring of trip coil of openeed CB
How is this done if the trip coil is isolated by 52a contacts as is normal?

RE: Trip coil supervision

For monitoring the trip coil of an open CB, a high resistance relay coil is connected in parallel to the trip contact, bypassing the 52a of the breaker. This relay is therefore energized continuously as long as the trip coil is intact, and the DC supply is intact. A NC contact on this relay is connected to the alarm.

Disadvantages:

1. The alarm will sound when a trip is activated.

2. A shorted trip coil cannot be detected.

rasevskii

RE: Trip coil supervision

Siemens 7PA30, three phase and single phase trip circuit supervision.

Go to:
7PA30

RE: Trip coil supervision

jghrist, isnt problem, we dont use additional relay, as
rasevskii  said.
Some resisitor about 30kOhm for 220V DC across a 52a contact.
current about 3-7mA, enough for supervision, voltage about 60V.
Isnt exactly, usually used NC contact of CB, etc...
This is a idea.
Used for decades.
Best Regards.
Slava
 

RE: Trip coil supervision

jghrist,

Here's one of the more common British trip circuit supervision relays, the GEC MVAX, which has some explanation of operation and some typical application circuits.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Trip coil supervision

Be careful of single pole devices. In one case I've seen where each pole had a monitor, and someone plugged in an AC powered relay for one of these. When it failed it only tripped one phase.

The new single pole capacitor breakers, that I know of, have an electronic module which monitors the trip coils, as well as manages the close functions. The second trip coils, are not controled by the module, and each coil should be monitored.

RE: Trip coil supervision

With three trip coils, all trip contacts should be in triplicate to prevent shorting out the monitoring function with a single relay trip contact feedign three trip coils in parallel.  Diode isolation of the three circuits can keep the monitoring in operation.

RE: Trip coil supervision

Yes,

you have to have three 74/TC trip coil supervision.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources