I am just wondering what some you are doing when sizing your fans to incorporate the friction loss of a filter. For instance I have a situation where I need 2000 cfm and a MERV 13 filter. When I go to the manufacturers literature I find that for 2000 cfm the pressure drop through a 2" filter is 0.4" wg. The literature also states that the final resistance is 1.0" wg. So when sizing your fan do you using the clean filter pressure drop (0.4"wg), the dirty filter pressure drop (1.0"wg) or somewhere in between?
Thanks.
Thanks.





RE: Filter Pressure Loss
RE: Filter Pressure Loss
RE: Filter Pressure Loss
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
RE: Filter Pressure Loss
I guess it depends on the application of the system.
For most applictions (office HVAC etc.) it is probably alright to size the fans for filters at halfway between new and dirty.
The difference between "half dirty" and "dirty" is probably only 75Pa and with a total fan-pressure of 1000Pa or so the difference in airflow is of little or no consequence in such an application.
But for a critical application where you need 100% flow under all circumstances you should size for dirty filters.
RE: Filter Pressure Loss
Put in a point for this information on the DDC.
Then, when complaints start about poor cooling/heating-stuffiness, you can find the problem right away.