short circuit tensile forces vs compressive forces

short circuit tensile forces vs compressive forces

short circuit tensile forces vs compressive forces

(OP)
Are the compressive forces acting on a 3 phase bus brace always less than the tensile forces? I say yes, but I am having a hard time to explain this to someone. Am I missing anything? This is my explanation – sum of current in three phases should be zero at any point of time. So, higher currents cannot flow in the same direction and induce a high compressive force.
Is there a way to calculate by what percent these force are lower?
Or am I just dumb and thinking in the wrong direction.
PLease help me understand better.

RE: short circuit tensile forces vs compressive forces

Zero-sequence currents all flow in the same direction at the same time.

RE: short circuit tensile forces vs compressive forces

(OP)
Is this true for a balanced 3 phase system?

RE: short circuit tensile forces vs compressive forces

Yes, for a ground fault.  

David Castor
www.cvoes.com

RE: short circuit tensile forces vs compressive forces

The forces on bus act to separate the phases.  This is true for 3Ø and Ø-Ø faults.  There are no forces between phases for 1Ø faults because there is current in only one phase.  There may be zero-sequence current in all phases, but except in the faulted phase, the positive- and negative-sequence currents are such that the total current is zero.  

Whether this causes compression or tension or cantilever in the braces depends on the geometry of the braces.

RE: short circuit tensile forces vs compressive forces

If there is a grounding transformer on the "load" side of the bus and a ground fault on the "system" side of the bus you can easily have the same zero sequence current in all three phases.

RE: short circuit tensile forces vs compressive forces

You would definitely have the same zero-sequence current in all three phases.  This is inherent in the definition of zero-sequence current.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources