Is it possible to operate generators in parallel which are connected in wye & delta? Assuming that all general requirements are met except that of their configurations..
thanks in advance
thanks in advance






RE: Paralleling of Wye-Connected & Delta-Connected Generators
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Paralleling of Wye-Connected & Delta-Connected Generators
RE: Paralleling of Wye-Connected & Delta-Connected Generators
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Paralleling of Wye-Connected & Delta-Connected Generators
How do you protect the delta-connected generator from ground faults? Since, it has no zero sequence current.
Regards,
RE: Paralleling of Wye-Connected & Delta-Connected Generators
If your sets are above 1000 KVA you probably want some advice from the fellows who work with the large sets such as ScottyUK.