oil field induction generator
Pumpjacks in the oil fields use 3-phase induction motors. During a certain portion of the pumping cycle, the weight of the falling masses can force the motor to rotate at above its synchronous speed, thereby turning it into a generator. There is a belief that this briefly (~ 1 second out of 5 seconds) generated energy can be passed to another motor in the same field, thereby slightly reducing the demand on the grid. For example, if the first motor generates 4 kW for 1 second and the second motor requires 20 kW during that time, the latter will receive 4 kW (less losses) from the first motor/generator and only need 16 kW from the utility.
What is the likelihood of this scenario?
1. The frequency of the generated energy is hard to predict. Let's say 61-62 Hz rather than 60 Hz. How well will it add with the 60 Hz from the utility?
2. The motors run at 460 V but the distribution to them is 12 kv. How well will the generated energy pass backwards through the step-down transformer at the first motor?
3. What losses should I expect if the 2 motor are 500 meters apart?
Thanks for your help.
RE: oil field induction generator
But, you need to correct your thinking about frequency. It stays at the grid's frequency (60 Hz) regardless of what your motors/generators do.
Gunnar Englund
www.gke.org
#2 As far as I know, the X-former won't care. Power will flow either way equally well.
#3 You have not provided enough information for a useful answer, a WAG is losses will be insignificant.
Also don't forget Murphy's law. There is a good chance that at some point the jacks will end up on the upstroke at the same time, so any reduction in "demand" will be negated.
If the meter is an electronic meter on the individual pump jacks you may be paying for the energy that you regenerate as well as the energy that you use.
Many electronic KWHr meters save KWHr consumption to one register and KWHr regeneration to a second register. The display, (what you pay for) is the sum of the two registers. This combats a popular illegal practice to steal energy.
This is the default setting of many electronic meters.
If there is any chance that you will be regenerating through a KWHr meter, you should discuss the situation with your utility. They may be willing to disable the reverse billing. The Public Utilities Commission may help. I doubt that their tariffs allow the utility to charge for regenerated energy.
Remember that when the weight is falling, the pump is lifting product. A balanced pump jack may be consuming energy to lift the weight and lower the piston and then be consuming energy to lift the piston and the column of product.
Bill
"Why not the best?"
Jimmy Carter
It's better to balance the jacks to lower the demand on each unit, which in turn will lower the overall metered demand.
Better than that, the lower demand will improve your overall voltage profile, which should lower your losses.
Thanks for pointing out my error regarding frequency. I assumed that the frequency of the generated energy would be a function of the speed of the overspeeded motor.
Yes, in this application, it is possible that the pumpjacks are not optimally balanced and are therefore generating during a portion of the stroke.
The meter is on the primary side. It meters several (or several dozen) pumpjacks. If several dozen, then there are always likely to be some consuming the energy that others generate.
Waross, I was intrigued by your description of the kWHr meter. Do you mean that if a pumpjack consumes 20 kWHr and generates 4 kWHr during an interval that I will be billed not for 20 kWHr, or 16 kWHr, but 24 kWHr?
The old electromechanical meters would run backwards on reverse power flow, but the new electronic meters typically sum all power flow, both forward power and reverse power.
I was talking to an old acquaintance recently who connected a small wind generator to the grid without permission. He was billed for the energy that he exported as well as the energy that he consumed.
Bill
"Why not the best?"
Jimmy Carter
With the electronic meters, they just did not read the generation quadrants of the meter. Again if the customer was not on file for generation.
This wasen't a bad policy, as a few customers would try to put cogeneration on, without the state mandated paperwork. There intent was to run the meter backwards, to get a better rate for there cogeneration.
If co-generation was approved, the defaults would be changed so that regenerated energy could be read separately. The default provided a hefty penalty for unauthorized regeneration. The original reason for the default setting is to combat one method of energy theft.
Bill
"Why not the best?"
Jimmy Carter