Strange fault event - 3 phase fault, Single phase fault or others
3

Strange fault event - 3 phase fault, Single phase fault or others

Strange fault event - 3 phase fault, Single phase fault or others

(OP)
All,

The following link contains a fault event graph. It shows that there was an event that ALL three phase currents were increasing for 4 ~ 5 cycles, however all three phase currents are in phase. During this event, C phase voltage is lower at 0.3 per unit. So, is it a single phase fault or three phase fault or others?  

What if there are multiple ground points at CT secondary and there was a nearby single phase fault, will the relay (SEL-351) see something like this?

Thanks for your opinion.
Regards,
Bing

RE: Strange fault event - 3 phase fault, Single phase fault or others

Single-phase to ground fault on c-phase.  Study your one-line of the local area and you'll find the transformer connections that make that possible.  What you've got is just zero sequence in all three phases.

RE: Strange fault event - 3 phase fault, Single phase fault or others

Quote:

Single-phase to ground fault on c-phase.  Study your one-line of the local area and you'll find the transformer connections that make that possible.  What you've got is just zero sequence in all three phases.
One place you'll see this is the line currents of a grounding transformer (zig zag or grd wye - delta) during a ground fault.
 

RE: Strange fault event - 3 phase fault, Single phase fault or others

(OP)

The transformer is Yg-Yg-D connection, and it is a wind farm. SEL-351 relay is at 115kV side and generation level is very low, about 1MVA. So, the Yg-Yg-D xmer is function as a grounding transformer for a fault at 115kV transmission line, so all three phases contains only zero sequence current.

Great! Thank you all for your help!  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources