Pavement distance around Substation fence

Pavement distance around Substation fence

Pavement distance around Substation fence

(OP)
thread238-138519: Step Potential Higher than Touch Potential ?

To mitigate risk of step and touch potential how far the pavement area shall be extended from substation fence? If we provide mesh of 3 feet outside fence, do we still have to extend pavement (with coarse stone 8 inch layer)outside fence?

RE: Pavement distance around Substation fence

If you don't extend the stone 3 feet outside the fence, then you have to use a reduced allowable touch-voltage outside the fence.  The mesh 3 feet outside the fence will reduce the touch-voltage, so meeting the reduced allowable may not be a problem.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources