Drain pipe design

Drain pipe design

Drain pipe design

(OP)
I am assigned to design a spill way for LNG tank. It is to drain LNG in case flange failure. While sizing the vertical drain piping, I was told to use self-venting design which limites froude # <0.3.

My questions are:

1. If design for full flow(froude # =0.8), is it acceptable? what bad will happen?
2. Is that necessary to design for self venting for this never or once in the tank lifetime scenario? The reason is the cost difference betw 12" and 20" SS pipe.

Thank in advance.

RE: Drain pipe design

(OP)
Any general practice in sizing drain piping is highly appreciated.
 

RE: Drain pipe design

The recommendations you will find for designing drains are MOST unlikely to apply to LNG.  Where do you want to drain the LNG to? How will you deal with flashing? Usually containment is more of a concern than draining it away. I am reluctant to give any recommendations on how to design such a drain without understanding the purpose of the design.  The drains from tank spillways are normally for draining rainwater, and not for the product contained in the tanks.

Katmar Software
Engineering & Risk Analysis Software
http://katmarsoftware.com

RE: Drain pipe design

As Katmar says, something sounds odd here.  Is this to limit pool fires in the event of a spill?

Taking it at face value that you want to drain LNG.  If the line isn't self venting the vapourising LNG would most likely vapour-lock the line, or at least massively restrict the flow.

As for whether it's necessary to design for a rare event, if you need this as mitigation for equipment failure, you need it to work.

Matt

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources